IR testing:
Live to Earth is only 0.01 mega ohms (10 KΩ) when testing at both 250V and 500V.

Live to Neutral and Neutral to Earth are both 200 mega ohms (250V), 500 mega ohms (500V).

Looks like it’s time to start lifting up floors and digging into walls to find the problem then.

At least you know what part of the circuit it’s on after splitting it down and IR testing it.
 
Would like to do that. But may not be practical as part of the cable is in the wall. If the connector was found (for example in a suspended ceiling), what next?
Take a photo of it and post it in dodgy trade pics thread.

then cut back the cable to the undamaged part and using correctly rated maintenance free connections repair it.
test
certify
give happy customer the invoice

goto local pub for a pint or local cafe for cheesecake
 
Take a photo of it and post it in dodgy trade pics thread.

then cut back the cable to the undamaged part and using correctly rated maintenance free connections repair it.
test
certify
give happy customer the invoice

goto local pub for a pint or local cafe for cheesecake
https://community.NoLinkingToThis/threads/extending-the-existing-6mm-cooker-cable.52161/

Yellow in line connectors:
 
I don't trust no-brand insulated crimps on 32A circuits. Plus, you'll need to join the 2.5mm² solid CPC and most crimps are not suitable for solid cores (some are, but they are specific types and you must use the matching tooling which can be £££)

Would suggest three Wago 773-173's which do 2.5 to 6.0. and are rated for 41A:
 
Continuity readings:
L E. 0.15 ohms
N E 0.88 ohms

Really ohms?

This thread started off all about moisture but now we get onto the actual readings they are perhaps 10,000 times lower than moisture is likely to be responsible for. Unless it's raining mercury?

That's a proper short-circuit you have there, a nail through the cable or similar, and all three conductors involved too.
 
Really ohms?

This thread started off all about moisture but now we get onto the actual readings they are perhaps 10,000 times lower than moisture is likely to be responsible for. Unless it's raining mercury?

That's a proper short-circuit you have there, a nail through the cable or similar, and all three conductors involved too.
Raining mercury, sounds mad as a hatter to me!!
 
Any recommendations on cable tracer?
Most will trace the wire. I presume the signal would weaken around the fault. There are loads on market from cheap to the expensive fluke 2042
I've not spent too much time looking at the current crop of cable tracers if I was in the market for one now it would probably be a Fluke or Ideal Industries unit

My goto for this type of fault would be my 3M cable tracer which was bought in the mid 80's and long since discontinued back then it cost around £500 and has well earned it's keep over the years, it operates on with voltages from 9 - 600v AC/DC so can be used on live and dead cables with a battery supply
 
Really ohms?

This thread started off all about moisture but now we get onto the actual readings they are perhaps 10,000 times lower than moisture is likely to be responsible for. Unless it's raining mercury?

That's a proper short-circuit you have there, a nail through the cable or similar, and all three conductors involved too.

Really ohms?

This thread started off all about moisture but now we get onto the actual readings they are perhaps 10,000 times lower than moisture is likely to be responsible for. Unless it's raining mercury?

That's a proper short-circuit you have there, a nail through the cable or similar, and all three conductors involved too.
I tested at fuse box end after connecting the live and earth at the other end. Same for neutral and earth.

Normal is about 0.72 ohms according to above.
 
Last edited:
So you have done a continuity test which is not that relevant to finding the fault you mention in the OP, you really need to be doing an IR check between the conductors
 
Are you saying you have done R1+R2 and R1+N ?
No. Just connected live and earth at switch end and then tested for continuity. Then similarly for Neutral, I connected neutral and earth at switch end before testing continuity at fuse box end.

I posted IR test results earlier.

I tested as shown in link below
 
So you have done a continuity test which is not that relevant to finding the fault you mention in the OP, you really need to be doing an IR check between the conductors
I was thinking: could continuity tests help to indicate whether fault is nearer the fusebox end or the other end.
 
No. Just connected live and earth at switch end and then tested for continuity. Then similarly for Neutral, I connected neutral and earth at switch end before testing continuity at fuse box end.

I posted IR test results earlier.

I tested as shown in link below
With both ends disconnected, the continuity reading is maximum ohms for all three tests: LE, NE, LN
 
Continuity readings:
L E. 0.15 ohms
N E 0.88 ohms
IR testing:
Live to Earth is only 0.01 mega ohms (10 KΩ) when testing at both 250V and 500V.
Live to Neutral and Neutral to Earth are both 200 mega ohms (250V), 500 mega ohms (500V).
With both ends disconnected, the continuity reading is maximum ohms for all three tests: LE, NE, LN

The continuity readings should be similar. If they are both correct (which they quite probably aren't) then the high one appears too high, because for 6mm² T&E cable R1 +R2 should be around 0.01Ω/m. 0.88Ω implies the cable is over 80 metres long which surely isn't correct. 0.15Ω looks entirely plausible, therefore the excess of 0.63Ω could indicate a high-resistance joint in the neutral that will heat dangerously under load (at 20A that's 252W, the heat of ten soldering irons)

The insulation resistance L-E at the fault seems to fall in the middle of the two ranges on the tester, off the bottom of the scale for IR (reading 0.01MΩ or lower (you can't tell how low when the display is showing the lowest possible number other than zero) but off the top of the scale for the continuity test. This is a limitation of most MFTs but we don't really need to know the actual resistance as it's definitely no good as it stands.

So what we can infer from the readings if they are all correct is that the insulation of the line is seriously low, possibly low enough to overheat dangerously, while the continuity of the neutral is seriously high, possibly high enough to overheat dangerously. The readings don't enable the location of the damage to be narrowed down.
 

Reply to Best way to deal with moisture in cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
13K
I'm reading a thread at the moment about a 9.8kW shower that has been installed on a 6mm cable. My natural instinct was to think that's wrong, it...
Replies
22
Views
6K
I do seem to pick only the weirdest properties to inspect... Victorian terraced house today - with up front RCD to a Wylex fuse board and main...
Replies
24
Views
3K
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
Replies
40
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock