Can someone tell me where in the new green book it gives the maximum disconnection time for a circuit on a TN system when there is likelyhood of contact from livestock? I just can't find it ?
Dichroic
don't think there is a specific time in the regs. however, 705.411.41... RCDs, so the disconnection times applicable to the RCD/s will apply.
Agricultural with contact with livestock not allowed a TN system, must be TT.
Section 7 something.
Edit: Sorry Tel's right
Reactions: 1 person
Thanks guys............to clarify;
Protection against shock may be provided by
1: ADS with additional protection by rcd (30ma) for final circuits supplying socket outlets rated at 32A or less.
2: ADS with additional protection by rcd (100ma) for final circuits supplying socket outlets rated at more than 32A.
3: ADS with additional protection by rcd (300ma) for all other circuits.
OR
by the use of SELV or PELV.
Where does it state that TN-S systems cannot be employed?
Regards
Dichroic
It doesn't, only a TN-C system is prohibited.
In locations intended for livestock, supplementary bonding shall be required.
See Tels post ^^^, it doesn't, it says TNC-S/PME is not recommended where there is no metal grid laid in the floor Sec 705.
And for ADS the 0.2s has been removed, replaced by the requirement of RCD's