Discuss BS7671 Green Book in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
dichroic
Can someone tell me where in the new green book it gives the maximum disconnection time for a circuit on a TN system when there is likelyhood of contact from livestock? I just can't find it ?
Dichroic
don't think there is a specific time in the regs. however, 705.411.41... RCDs, so the disconnection times applicable to the RCD/s will apply.
Thanks guys............to clarify;
Protection against shock may be provided by
1: ADS with additional protection by rcd (30ma) for final circuits supplying socket outlets rated at 32A or less.
2: ADS with additional protection by rcd (100ma) for final circuits supplying socket outlets rated at more than 32A.
3: ADS with additional protection by rcd (300ma) for all other circuits.
OR
by the use of SELV or PELV.
Where does it state that TN-S systems cannot be employed?
Regards
Dichroic
See Tels post ^^^, it doesn't, it says TNC-S/PME is not recommended where there is no metal grid laid in the floor Sec 705.
And for ADS the 0.2s has been removed, replaced by the requirement of RCD's
Reply to BS7671 Green Book in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
OLDBOY
O
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...