Can someone tell me where in the new green book it gives the maximum disconnection time for a circuit on a TN system when there is likelyhood of contact from livestock? I just can't find it ?

Dichroic
 
don't think there is a specific time in the regs. however, 705.411.41... RCDs, so the disconnection times applicable to the RCD/s will apply.
 
Thanks guys............to clarify;

Protection against shock may be provided by

1: ADS with additional protection by rcd (30ma) for final circuits supplying socket outlets rated at 32A or less.
2: ADS with additional protection by rcd (100ma) for final circuits supplying socket outlets rated at more than 32A.
3: ADS with additional protection by rcd (300ma) for all other circuits.

OR

by the use of SELV or PELV.

Where does it state that TN-S systems cannot be employed?

Regards

Dichroic
 
Where does it state that TN-S systems cannot be employed?

See Tels post ^^^, it doesn't, it says TNC-S/PME is not recommended where there is no metal grid laid in the floor Sec 705.

And for ADS the 0.2s has been removed, replaced by the requirement of RCD's
 

Reply to BS7671 Green Book in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
419
OLDBOY
O
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
200
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
791
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock