Hello,

The layout for my kitchen, which is not installed yet, is such that there is a free-standing dishwasher and washing machine on either side of a cupboard which has the kitchen sink over it.

My builder who recently re-wired my house has installed the wiring so that the plug sockets for these two appliances will be inside this under-sink cupboard as opposed to being on the wall behind each appliance.

Is this safe? To me is sounds dangerous to have plug sockets under a sink like this.

I have attached a diagram to help illustrate the situation.

Thanks

diagramPlugSocketPlacement.png
 
This isn't usual and infinitely better than having the sockets behind the appliances.

What does your builder say on the matter, or should I say the builders spark?
 
Yes it's okay, its something I do on a regular basis. Consideration should be given as to where the sockets are mounted, in terms of accidental leaks and if fixed to the floor unit, to a substation wood panel. Sometimes my customers also prefer an additional means of isolation above the work top in the form of a double pole switch, I would normally recommend this option. It would also be the only option in a new build.

I can understand your concern with leaking pipes/waste, but the same could be said about the possibility or potential in the rest of your property.

Placing a socket behind an appliance, makes it difficult for maintenance purposes (changing the plug top fuse etc), and you may find there will be insufficient room to push back the appliance, with socket & plug top behind it. What did you agree with your builder before work began? And I hope it was an electrician who did the alterations, not the builder!

Ps pipped to the post
 
Thanks @Murdoch and @Midwest

It was my builder's Electrician who did the work but I am dealing with my builder so haven't spoken to the Electrician.

There was no agreement before he began. He wired it up like this before even seeing the plans for the kitchen and I had thought he would ask me for them before he went onto this stage but he just did it like this without asking for them.

My builder said much the same as you two re. can't have sockets behind as not supposed to have to move the appliance to turn it off.

I just have always been told about not mixing water and electricity and can't ever recall seeing plug sockets under sinks/next to water pipes etc. so I was concerned but from both of your replies it seems this is a safe/standard practice.

Thanks
 
Thanks @Murdoch and @Midwest

It was my builder's Electrician who did the work but I am dealing with my builder so haven't spoken to the Electrician.

There was no agreement before he began. He wired it up like this before even seeing the plans for the kitchen and I had thought he would ask me for them before he went onto this stage but he just did it like this without asking for them.

My builder said much the same as you two re. can't have sockets behind as not supposed to have to move the appliance to turn it off.

I just have always been told about not mixing water and electricity and can't ever recall seeing plug sockets under sinks/next to water pipes etc. so I was concerned but from both of your replies it seems this is a safe/standard practice.

Thanks

It is within the regulations which is the important bit. The regulations ask for environmental effects likely to be encountered to be considered. As a sink is not designed to leak then it is not really a consideration.
Personally I have seen many leaking appliances that have affected sockets directly behind the appliances, but not so many affected under sinks.
 
came acroos a CU mounted directly below the kitchen sink in a 1970 built house. fitted like that as new. 46 hears on, no dasmage to CU.
 
It is within the regulations which is the important bit. The regulations ask for environmental effects likely to be encountered to be considered. As a sink is not designed to leak then it is not really a consideration.
Personally I have seen many leaking appliances that have affected sockets directly behind the appliances, but not so many affected under sinks.
Thanks, that's good to know.
 
It is my preferred option to kit plug sockets in cupboards as I am of the opinion that it is more pleasing on the eye than having switches or fused connections above the worktop or behind the appliances where room may be tight, specially in smaller kitchens. I always discuss the option of putting switches above the worktop with the client though and let them make the choice.
 
Double post?

Dunno whats going on here. First double post then the one I posted in disappears?

Anyhow, agree with you rolyberkin. But sometimes DP are advantages with elderly people for example, and easier to isolate the washing machine when it starts going off on one, and keeps tripping the RCD. Its what the customer prefers I suppose.
 
Last edited:
Back to the op, make a point of meeting the spark and getting his card so you know to find him later....

I always prefer to meet the client early on and always leave them my card.
Don't think I will get the chance to meet the Electrician now but my builder says he has the certificate from him so I assume his details will be on that, is that correct?
 
Yes all the electricians details will be on the electrical installation certificate, just to add to the other posts there's nothing wrong with fitting a socket outlet in a base unit under the sink , think of an electric shower for example where water and electricity are in very close proximity. I tend to fit such sockets on the side panels and near the front of the cupboard to make accessibility easier and reduce the chance of them being accidentally switched off by bits and pieces rammed into the cupboard.
 
Don't think I will get the chance to meet the Electrician now but my builder says he has the certificate from him so I assume his details will be on that, is that correct?

Hum.... I looked at your previous thread and is this socket the one where the cable was run behind the skirting board?

and if so, its in the wall, and as the kitchen is not yet fitted, does the builder plan to leave the back off the the base unit? That's going to look pants!
 
Hum.... I looked at your previous thread and is this socket the one where the cable was run behind the skirting board?

and if so, its in the wall, and as the kitchen is not yet fitted, does the builder plan to leave the back off the the base unit? That's going to look pants!
Hi, he's left a loop of wire which he says will be for a double socket to be placed in the back of the base unit, so think this is OK. Thanks for spotting this.
 
Hi, he's left a loop of wire which he says will be for a double socket to be placed in the back of the base unit, so think this is OK. Thanks for spotting this.

In which case the electrics are NOT complete and therefore I would question the fact the builder says he has the "certificate(s)"
 
In which case the electrics are NOT complete and therefore I would question the fact the builder says he has the "certificate(s)"
Ah, he did say that because the wire has been left in a loop he was able to get certificate for it and had it been cut he wouldn't.

I suppose that whoever I get to install the kitchen will have to cut the loop, attach it to plug socket and mount in the cupboard. Would it then just be a case of the Electrician who does this self-certifying that all is OK with his work and because the work done previously to this has certificate all is OK?
 
The circuit needs testing and certifying after ALL work on it is complete. Daz
 
The circuit needs testing and certifying after ALL work on it is complete. Daz
I think his thinking is that as is a loop it could technically be left like that and so even though need aforementioned plug socket/s added, I suppose at later date now, it is complete in a way and so certificate has been done. Does this make sense/is a technical way of getting round this?
 
I think his thinking is that as is a loop it could technically be left like that and so even though need aforementioned plug socket/s added, I suppose at later date now, it is complete in a way and so certificate has been done. Does this make sense/is a technical way of getting round this?
He could, but then the new electrician would need to complete a minor works cert to add the new socket.

PS but a lot of electricians would just put in the new socket on that loop, probably with no cert ;)
 
Last edited:
I think his thinking is that as is a loop it could technically be left like that and so even though need aforementioned plug socket/s added, I suppose at later date now, it is complete in a way and so certificate has been done. Does this make sense/is a technical way of getting round this?

I am losing the plot on this, are you the spark?

No decent spark signs of an incomplete installation and gives the cert to the builder....... I doubt there is a competent spark involved
 
I am losing the plot on this, are you the spark?

No decent spark signs of an incomplete installation and gives the cert to the builder....... I doubt there is a competent spark involved
Yeah I am a bit worried this might be what is happening because of 2 other things:
1. In the kitchen there is a normal light bulb placed in the ceiling (no cord hanging down - straight into the bayonet/fixing) but I think the builder said previously that can't have those sort of light bulbs in kitchen any more but nonetheless it is there and he says has cert.
2. He told me that a wire for a socket will be re-routed and placed directly into the fuse-board/box yet he said this would be done at same time he said already has the certificate for the whole job.
 
It is my preferred option to kit plug sockets in cupboards as I am of the opinion that it is more pleasing on the eye than having switches or fused connections above the worktop or behind the appliances where room may be tight, specially in smaller kitchens. I always discuss the option of putting switches above the worktop with the client though and let them make the choice.
Is above counter isolation not an English building reg requirement? It is in Scotland. Socket outlets in cupboards are in my humble opinion shiiiite. Might well comply but smacks of kev the kitchen fitter doing the wiring. Just my opinion though.
 
Is above counter isolation not an English building reg requirement? It is in Scotland. Socket outlets in cupboards are in my humble opinion shiiiite. Might well comply but smacks of kev the kitchen fitter doing the wiring. Just my opinion though.

In a new build or major refurbishment, perhaps yes to comply with Part M Building Regs 'to assist people who have reduce reach'. But it only specifies min & max height of switches etc. Designers of new builds often use the central set of DP switches. What do the Building regs in Scotland state?

As regards socket outlets in cupboards, how else do you supply an appliances?
 
Is above counter isolation not an English building reg requirement? It is in Scotland. Socket outlets in cupboards are in my humble opinion shiiiite. Might well comply but smacks of kev the kitchen fitter doing the wiring. Just my opinion though.
Maybe, but there's a lot to be said for them:
There's only one fuse per appliance.
If sensibly positioned, then isolation by switching off or unplugging is easy.
It's usually more obvious which appliance is being served than some arrangements of SFCUs I have seen.
Easy access for fixed wiring test and inspection. (No hidden accessories.)
Easy to access the plug for ISITEE.
 
I'd agree in cupboard sockets for appliances is neater than above counter isolators. I don't like a kitchen littered with sockets and switches for appliances all round the edge. Neater out of the way and still possible to mount above 450mm to be complaint.
 
Not if you have a disability which reduces your reach, think that's why we see those centrally located DP switches on new builds.
Isn't a switch inside a low cupboard at 450mm high easier to reach than an isolator above the work top? With its 600mm depth to reach over?
 
If the kitchen is specifically for disabled access there are detailed guidelines on access and positioning.
 
In a new build or major refurbishment, perhaps yes to comply with Part M Building Regs 'to assist people who have reduce reach'. But it only specifies min & max height of switches etc. Designers of new builds often use the central set of DP switches. What do the Building regs in Scotland state?

As regards socket outlets in cupboards, how else do you supply an appliances?
Scottish Regs stipulate isolation switch above counter top for under counter appaliances. I always put Socket outlets behind the appliance fixed to the structure of the building. Regs are to be followed whether a new build or old.
 
Scottish Regs stipulate isolation switch above counter top for under counter appaliances. I always put Socket outlets behind the appliance fixed to the structure of the building. Regs are to be followed whether a new build or old.

Probably based on the assumption that the actual socket will be inaccessible which it certainly will be behind a snug fitting and heavy washing machine for example ! And if the fuse in the plug top should fail then anyone elderly or infirm will never get to it without assistance ! Yes regs should be followed but a modicum of common sense doesn't do any harm either. :)
 
Got to agree with DaveOCD - what's the point in a plug/socket behind a washing machine. Once the fuse blows no-one can get to it. Daz
 
Ok then; I expect the later easier if your in a wheelchair or elderly & infirmed:)
Yes that makes sense. If the elderly or infirm need to pull the appliance out to do a quick repair its easier if the socket is counter top. Can't imagine they'd get somebody able to do that for them.
I agree for items like kettles toasters etc then counter top of course. But an isolator for an appliance normally only gets used when there's a problem. Should an appliance burst into flames having the isolator above and behind it isn't really much help.

I also agree there is little point in sockets behind appliances.
 
Yes that makes sense. If the elderly or infirm need to pull the appliance out to do a quick repair its easier if the socket is counter top. Can't imagine they'd get somebody able to do that for them.

Should an appliance burst into flames having the isolator above and behind it isn't really much help.

I also agree there is little point in sockets behind appliances.

Not suggesting the appliance socket should be above the worktop. I was suggesting a DP switch above a worktop would be more accessible for persons with restricted reach, for turning off the appliance, either in the circumstances you describe above or because they feel inclined to.
 
Scottish Regs stipulate isolation switch above counter top for under counter appaliances. I always put Socket outlets behind the appliance fixed to the structure of the building. Regs are to be followed whether a new build or old.
Only in Scotland does this 'reg' appear to apply.
 
I have seen appliance instructions which state not to install in front of a socket outlet. I assume that it's because the back of the appliance gets warm, which might affect the plug. (Think it was a dishwasher.)
 
Agree with Midwest - as soon as you start with flex outlet plates then it's a sparky job to connect/disconnect. Daz
 
Oh come on now. Any appliance repairer will be capable of isolating an appliance and using a flex outlet, a cooker connection plate, or a FCU for disconnection of an appliance. If they are having to call an electrician for that they are in the wrong job.
 
Don't know about you but I don't want some heavy handed appliance swapper removing my FCU and disturbing the connections. Of course he'll test the ring end to end values afterwards. Won't he? Daz
 
Oh come on now. Any appliance repairer will be capable of isolating an appliance and using a flex outlet, a cooker connection plate, or a FCU for disconnection of an appliance. If they are having to call an electrician for that they are in the wrong job.
You giving too much credence to these 'engineers'.
 
Don't know about you but I don't want some heavy handed appliance swapper removing my FCU and disturbing the connections. Of course he'll test the ring end to end values afterwards. Won't he? Daz
What anyone does with an installation after I have completed the job is really nothing to do with me.

You giving too much credence to these 'engineers'.
I never called them engineers :D
I have met quite few and most are competent to be doing their job, a large part of which is using fixed wire connections.

Connection plates are there to provide a point to connect to for a competent person, and part of an appliance installer/repairer's job is to connect appliances.
 
Well I've had calls from customers where they've paid companies for delivery and 'installation' of kitchen appliances only to be told that they can't connect as they're not insured or other such excuse - always flex outlet plates or SFCUs.
 
Well I've had calls from customers where they've paid companies for delivery and 'installation' of kitchen appliances only to be told that they can't connect as they're not insured or other such excuse - always flex outlet plates or SFCUs.

Like I said, most are competent. But most is not all.
 

Reply to Can Plug Sockets for Dishwasher and Washing Machine be Placed in Under-sink Cupboard? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Sorry two questions today. We had the kitchen rewired based on existing units, but with a slightly new layout it puts the dishwasher right over...
Replies
1
Views
746
Hi there, I have two isolation switches above a kitchen workcounter. They currently turn off the power to a pair of unswitched sockets which are...
Replies
2
Views
3K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K
Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock