Hi, I have a customer who has bought a 7Kw hob to compliment a 4.8Kw double oven. He didn't realise the extra power consumption would put additional loading on the existing 6mm cable. My initial response was to tell him that an additional circuit was required and due to locations of consumer unit and hob it won't be straightforward
However I looked at diversity regarding cooking appliances and 51amps loading reduces to 23 or 28 amps which is within the capacity of the existing wiring.
I will probably still go with the additional circuit but what's the point of having diversity if we don't apply it. Thanks for your thoughts.
 
Whats the point of cable and current carrying capacities if you are then going to disregard all the evidence and recommendations to then make up your own presumptions and install extra cable where none may be required
 
What is irritating is when you could easily install oven/hob on 1x 6mm2 supply, but they are located on opposite sides of the kitchen!
 
What is irritating is when you could easily install oven/hob on 1x 6mm2 supply, but they are located on opposite sides of the kitchen!
extension lead? :mad:
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Cooking appliances. Diversity versus practice
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
treehouse,
Last reply from
Octopus,
Replies
6
Views
2,407

Advert