I recently came across a video on YouTube and the guy fit a fuseboard. Very tidy job but I was confused as he used couplers to have the board not flush with the wall and there was massive holes in the back where the cable comes through.
1) doesn't it need to be ip rated so nobody can get there hands in?
2) doesn't it need to be fire rated?

Just posting this as I want to know if there is a flaw in my thinking somewhere. Here is the link to the video -
 
Have seen quite a few YouTube celeb Sparks space off a board from the wall using conduit couplers or a 2 inch off cut of pipe for example. Giving them a nice space to bring all the cables round under the board and in Via the back.
A consumer doesn't need to be Fire Proof / Rated. It needs to be constructed from non-Combustible material e.g Metal.
If it is spaced so far off a the wall that you can reach your fingers underneath and poke your fingers in Via the back then it would fail on IP rating. I believe sides and back must be IP2X. But from a Video its hard to tell how far one can poke your fingers inside.
Much will depend on how skinny your wrist is and how long your fingers are I guess.
 
Much will depend on how skinny your wrist is and how long your fingers are I guess.
Or preferably this (example)!
IMG_0133.jpeg
 
I do like to space a board off the wall a bit for 2 main reasons...

1, it allows you to bring all the cables in from the back and thus keep all the sides intact
2, often garage walls are not straight so by spacing off the wall a bit you avoid having a twisted board

An inch off the wall there is no real someone can get all their fingers into the rear knock-out, not unless they have incredibly long fingers
 
Wouldn't it be being able to touch live parts with a standard finger and not just accessing the board? Going through the back is usually much simpler in domestics.

I prefer the busbars to have a cover instead of the the barriers like in the fusebox boards, some of the better ones are IP2X with the cover off.
 
I recently came across a video on YouTube and the guy fit a fuseboard. Very tidy job but I was confused as he used couplers to have the board not flush with the wall and there was massive holes in the back where the cable comes through.
1) doesn't it need to be ip rated so nobody can get there hands in?
2) doesn't it need to be fire rated?

Just posting this as I want to know if there is a flaw in my thinking somewhere. Here is the link to the video -
He should have fitted SP+N rcbos as an N to E fault could still trip others.
 
Any ideas on what would cause that?
Neutral earth faults where you can get circulating currents, particularly on tncs systems

Unless you disconnect the Neutral, the fault is going to remain
 
Last edited:
Is this something you have experienced? I don't generally fit DP rcbos. I like that they make ir testing easier but I don't feel it's worth the extra expense.
If you consider how long the CU is going to sit there, the extra cost is pretty negligible really. And they don't twist as much (thinking Fusebox)

Consider this scenario:
Lighting circuit has N-E fault as outside light filled up with water.
Cooker circuit with no faults.
Both RCBO's on.

Turn on Cooker, the return current has an extra path via the fault in the lighting. If the N-E resistance is low enough one or both of the RCBO's will trip. So far that is exactly the same whether SPSN or SP RCBOs.

The benefit to the customer of the SPSN is that over the phone I can now diagnose it and as long as the SPSN lighting RBCO is off they can now turn the cooker back on and make their kippers on toast. If we skimp and fit SP RCBO's the faulty N path remains and they have to learn to like spam sandwiches.

One could argue that (specifically) for tolerance of N-E faults a fully loaded SP RCBO board is even worse than a dual RCD board.
 
Last edited:
If you consider how long the CU is going to sit there, the extra cost is pretty negligible really. And they don't twist as much (thinking Fusebox)

Consider this scenario:
Lighting circuit has N-E fault as outside light filled up with water.
Cooker circuit with no faults.
Both RCBO's on.

Turn on Cooker, the return current has an extra path via the fault in the lighting. If the N-E resistance is low enough one or both of the RCBO's will trip. So far that is exactly the same whether SPSN or SP RCBOs.

The benefit to the customer of the SPSN is that over the phone I can now diagnose it and as long as the SPSN lighting RBCO is off they can now turn the cooker back on and make their kippers on toast. If we skimp and fit SP RCBO's the faulty N path remains and they have to learn to like spam sandwiches.

Once could argue that (specifically) for tolerance of N-E faults a fully loaded SP RCBO board is even worse than a dual RCD board.
You could always fit DP mcbs. into a split load CU.
 
Turn on Cooker, the return current has an extra path via the fault in the lighting. If the N-E resistance is low enough one or both of the RCBO's will trip. So far that is exactly the same whether SPSN or SP RCBOs.
With single/dual RCD yes, but not RCBO unless it has an up-front RCD (as sometimes done for TT systems). For RCBOs to interact in a non-obvious manner it would need to be a N-N sort of fault.

The N-E fault tripping out other circuits happens because of the common RCD to several MCBs in older board. Basically as far as that RCD is concerned they are all the same circuit.

I would always go with DP (SP + N) RCBOs if I could as they make testing easier. But where it really matters is systems with RCDs higher in the supply chain, such as TT with incomer RCD, or a farm with 300mA RCD for fire safety reasons, or sub-main where you can't disconnect in time simply on Zs, etc. Without switching N there you don't have proper selectivity and any N-E fault will trip out the upstream protection.
 
With single/dual RCD yes, but not RCBO unless it has an up-front RCD (as sometimes done for TT systems). For RCBOs to interact in a non-obvious manner it would need to be a N-N sort of fault.
I agree with you that I was wrong about which device will trip, I wasn't thinking straight. The "large load" RCBO (not shown) will not trip as everything "coming in" is also "going out".
But I think my wider point is correct - this kind of thing can still happen (supply at top, large load with own RCBO on left, another RCBO with faulty circuit on right).
And with a SP+N RCBO the customer can isolate the fault until someone can come and prod it.

1683804411827.png
 
Consider this scenario:
Lighting circuit has N-E fault as outside light filled up with water.
Cooker circuit with no faults.
Both RCBO's on.

Turn on Cooker, the return current has an extra path via the fault in the lighting. If the N-E resistance is low enough one or both of the RCBO's will trip. So far that is exactly the same whether SPSN or SP RCBOs.
Eh? I don't understand how this would work...

Resize_20230511_123441_1678.jpg

If you have an upstream (e.g. time-delayed) RCD then sure, you need the RCBO to disconnect the N so that it clears as well as detects the fault. But if there is no upstream RCD, you're fine... surely?

EDIT: just seen your later post, fair enough! :)
 

Reply to Fire rating of fuseboard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
im not sure where to post this.. and I need help [ I posted here because i guess Heating systems may need a hole this big , and this is the only...
Replies
16
Views
1K
Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K
You might remember this delight from the dodgy trade pictures thread.... I finally got back to quote for sorting today. The chicken and egg...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock