I am installing a Teletask Micros+ metal enclosure

Is it ok to bring just Live and SW Live conductors though a 400mm by 20mm slot cut in the rear of the enclosure ( sometimes cut in the base )

I know I have to bring L N CPC conductors through the same hole but the N and the CPC conductors are all terminated in the large plastic trunking which is mounted underneath the panel to keep it neat & because there is not enough room in the metal panel for them all




Thank you
 
thank you for the quick reply

I forgot to say the panel has a 3 core mains flex which powers the power supply which earths the panel & an internal earth bonding point

I was worried about regs ( 521.5.1 Ferromagnetic enclosures: electromagnetic effects )

this is the panel https://www.teletask.be/media/2454/tds10012_en.pdf

Thank you

Paul
 
I believe that with live only, into and out of the metal cabinet, a magnetic field will be generated around that conductor and circulating currents will be induced into the metal enclosure around the conductor,it could result in a build up of heat if that cable was passing a high current
 
I believe that with live only, into and out of the metal cabinet, a magnetic field will be generated around that conductor and circulating currents will be induced into the metal enclosure around the conductor,it could result in a build up of heat if that cable was passing a high current

Surely if you've a line in and a switched line out the same hole, the magnetic effects of the cables are cancelled out by each other.
 
I believe that with live only, into and out of the metal cabinet, a magnetic field will be generated around that conductor and circulating currents will be induced into the metal enclosure around the conductor,it could result in a build up of heat if that cable was passing a high current

Only happens when the current returning passes through a separate hole in a ferrous enclosure.

Surely if you've a line in and a switched line out the same hole, the magnetic effects of the cables are cancelled out by each other.

Correct.
 
  • Like
Reactions: Des 56
Put a pvc gland on i
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
just live & S/L conductors in a metal enclosure ?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
streetlighter 1,
Last reply from
stummish,
Replies
9
Views
1,683

Advert