Afternoon all,

As title suggests I’m not sure if such a product exists but I’m looking for a 20amp contactor that is mounted into a single box/patress

Reason being another sparks has wired 2 ufh mats 1800w each onto a single spur (14-16amp)
 
why not. it's rated for it? and if you have "proper" voltage of 240V, it's 15A. beaRING IN MIND THAT IT'S INTERMITTENT AS THE STAT. SWITCHES OFF WHEN THE SET TEMP. HAS BEEN ACHIEVED.and the bloody caps lock right next to the "A". stupid layout. should have been put by the Q or the Z.
 
I would agree with you but it’s never good to be running it at 100% 24/7


There is also the potential although unlikely to go upto 16.36amp

Thermostat is currently tripping rcbo if trying to run both mats
 
why not. it's rated for it? and if you have "proper" voltage of 240V, it's 15A. beaRING IN MIND THAT IT'S INTERMITTENT AS THE STAT. SWITCHES OFF WHEN THE SET TEMP. HAS BEEN ACHIEVED.and the bloody caps lock right next to the "A". stupid layout. should have been put by the Q or the Z.
No wonder 'ring in mind' jumped out at me.....
 
Afternoon all,

As title suggests I’m not sure if such a product exists but I’m looking for a 20amp contactor that is mounted into a single box/patress

Reason being another sparks has wired 2 ufh mats 1800w each onto a single spur (14-16amp)
Good luck with your search please keep us informed.
 
If you're driving a heating load, what about a SSR?
RS Pro 25A SSR 90-240Vac control
or similar would seem ok and are quite compact to be tucked into a box?

NB: I'm not up on any UK regs that would cover or prohibit the use of such industrial gear in a home. You would definitely want upstream isolation for maintenance, as SSR can fail closed if shorted.
 

Reply to Looking for contactor that fits in single box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am helping with some village lights and need some advice as to a route forward (our electrician is unavailable for an undefined period) We...
Replies
6
Views
2K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use...
Replies
38
Views
7K
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock