Discuss Minor Works and Meter Tails in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Even if its not as per the regs ?? they recommend 25mm
I'd more more interested in making sure the earthing/bonding is correct.
What's the CCC of 16mm tails? ;)
If I was replacing a CU then perhaps you would but I don't see the point to be honest.
If the customer doesn't want to pay then why do it?
Bonding is fine and up to date, The 16mm tails will carry roughly 85 amp so im not bothered about that.. its a case of weather its acceptable to issue MWC if the tails are not as per the regs
You wouldn't find me changing them, you've just proved yourself that they do not need to be. 16mm tails rated to 85A protected with 60A device, where's the issue?
What earthing system is the installation using?
Its a TNCS, just beating myself up with the regs as they state minimum 25mm
As I keep seeing posted recently, the Regs are Guidance Notes NOT LAW. In this situation you can safely justify why they do not need to be replaced especially as you are only doing a Minor Works. CU change? Fair enough but the customer has already stated that they do not want to pay for it.
Reply to Minor Works and Meter Tails in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...