Hey guys,
I’m Marc, admin over on the tilers Forum. :D

Quick question if I may please.
In middle of Tiling shower area in an ensuite and the electrician has put a fused spur opposite the shower head for a towel rail, can you tell me if this is within regulations please.
The distance between each wall is 2.35m and I’ve attached an image to show its position.
The red circle right side shows the spur location.
Thanks very much.

8BED135D-716B-446A-9D9B-947990EA515E.jpeg
 
> 0.6m from edge of shower tray will comply (out of zones).. if there's any danger of water splashes to the FCU< then a IP rated one should be fitted.
 
  • Like
Reactions: 3_fall
is that a door way near the S/F by any chance?
 
Last edited:
it's not a doorway, it's a portal into another dimension.
 
What putting the FCU outside the ensuite, and flex outlet plate inside. Just in case the FCU gets showered, and house owner turns it on stood in pool of water, silly billy.

Incidentally Marc, those tiles look cracked to me, or someone's not been careful with their hob nail boots :)
 
i'm just wondering why there's a climbing wall there.
 
  • Like
Reactions: Pete999
It is fine but I would have the FCU outside the room and then an outlet plate for the rail ................
Done that plenty times too but not always possible.

Is an outlet plate any better in terms of IP ratings than an unswitched FCU though?
 
It is fine but I would have the FCU outside the room and then an outlet plate for the rail ................

I already suggested that in #10? Am I just farting in space.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
3_fall,
Last reply from
Midwest,
Replies
23
Views
2,083

Advert