Not much to it in all honesty. Put a rod in as even if its TNS at the property, you need the dno to confirm its TNS back to transformer/sub station. They seem very reluctant to give this confirmation. So with the 18th edition ruling out PME in any case. Its best to just plan the job from the start with intent to put a rod in.