After having the shower circuit upgraded to 10mm cable, new shower and pull switch the tripping times recorded for the existing rcd are as follows.
76ms x1 65ms x1(180) 28.6ms x5 38.3ms x5 (180). These times appear not to meet the standards for the minor works cert and im after suggestons as to my options. The existing rcd is about 10 years old and on asking the occupier has not carried out regular operation through the test button. I know the easy answer is to change the rcd, but is there something else that could be causing this that i can consider.

look forward to you suggestions
 
within BS7671 values, what's the problem? have you tried testing at the RCD with no loads connected?
 
Hi all

After having the shower circuit upgraded to 10mm cable, new shower and pull switch the tripping times recorded for the existing rcd are as follows.
76ms x1 65ms x1(180) 28.6ms x5 38.3ms x5 (180). These times appear not to meet the standards for the minor works cert and im after suggestons as to my options. The existing rcd is about 10 years old and on asking the occupier has not carried out regular operation through the test button. I know the easy answer is to change the rcd, but is there something else that could be causing this that i can consider.

look forward to you suggestions

Have a think about it..................and while you are have a look on page 295 of the regs and table 3A ....................
 
hi all

checked the regs and happy with the results now. Getting mixed up with the results and how they fit the allowances. Happy they are within 300ms and 40 ms. still learning but getting there.

Thanks for the advice
 

Reply to poor rcd tripping times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon all, As we all know the new 18th certs only have the facility to record the x1 trip time of a circuits RCD in the test results page...
Replies
4
Views
27K
Deleted member 26818
D
On completion of some recent minor work , I carried out the usual testing and noticed the incoming 100A 30mA rcd on the Consumer unit was failing...
Replies
33
Views
4K
1
Hi Guys, Have seen some similar threads on these boards but still after some wisdom . . . At clients yesterday and completed tests on a lighting...
Replies
4
Views
5K
Octopus
O
My mrs recently new bezzy girl mates partner has some property, my mrs said, " my hubby do it for ya at a good rate " joy i think. I had this...
Replies
103
Views
8K
specs
S
I always been told that an 30m/A RCD should trip within 200m/s (x1) and 40m/s (x5). But something iv never taken much notice of before is on test...
Replies
27
Views
25K
Engineer54
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock