• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members

Discuss Protection against open/loose neutral? in the American Professional Electrical Advice Forum area at ElectriciansForums.net

Hello friends, is there such a thing as a "smart meter" that I can install on my backwoods house that will trip if it detects a loose/open neutral? If so, where can I get one? Thanks very much
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members

Megawatt

-
Arms
Advent Win
Hello friends, is there such a thing as a "smart meter" that I can install on my backwoods house that will trip if it detects a loose/open neutral? If so, where can I get one? Thanks very much
Hello Kevin and welcome to the forum and yes they make smart meters but that’s the meter the power company puts in. The meter is called a smart meter because the power company can read it without ever coming on your property. Are you having some kind of problem that you need help with. You can buy GFCI breakers that could do what you want
 

Lucien Nunes

-
Mentor
Arms
Esteemed
A high resistance neutral connection is usually manifest by incorrect voltages - on a single (split) phase supply one hot-neutral voltage goes up (the one with more load) and one goes down while the hot-hot voltage is unaffected, similarly for 3-phase.

This is easy to detect; for example you can buy voltage-sensing relays that can be set to trigger an output when the voltage goes beyond settable limits for a certain duration. These could then operate a shunt-tripping add-on unit to a main breaker, to isolate your panel from the faulty supply. (There are complications in practice, such as making this run from the hots only, so that the failed neutral doesn't stop the protection working).

Perhaps there is an all-in one unit? As MW says, is this a precaution or are you experiencing equipment damage from repeated loss of your neutral? For small loads, certain types of UPS will protect them against excessive voltage.
 

Megawatt

-
Arms
Advent Win
A high resistance neutral connection is usually manifest by incorrect voltages - on a single (split) phase supply one hot-neutral voltage goes up (the one with more load) and one goes down while the hot-hot voltage is unaffected, similarly for 3-phase.

This is easy to detect; for example you can buy voltage-sensing relays that can be set to operate an output when the voltage goes out of range. These could then operate a shunt-tripping add-on unit to a main breaker, to isolate your panel from the faulty supply. On the more sophisticated ones you can set the thresholds and delay time to minimise nuisance trips on start-up surges etc.

Perhaps there is an all-in one unit?
I got to admit that you are pretty sharp on electrical, are you some sort of engineer.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
are you some sort of engineer.
Yes, although I've long since forgotten which sort!
 