Discuss Range Oven Isolator Position Deemed Code 1 on a PIR ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Finally got through but it looks like its down to which regulation you are applying to the isolator.
The definition between an isolator for mechanical maintenance and an isolator for emergency switching would need to be verified through a risk assesment.
I have also spoken to an old safety officer friend, with an electrical consultant I know, and also a fire officer.
One thing is definate, its not a code 1.
As far as a code 2 is concerned. That could actually be applied if it can be proved that the isolation was for emergency purposes.
The primary reason would be to remove a source of ignition following a fire.
The grey area here is most, including fire officers would deem the controls on the front of the appliance suitable for this purpose in most cases.
Concensus seems to be life is more precious than property so GET OUT. The consumer unit is the next viable means of isolation, in any event.
To complicate or maybe help to define the position further (Depending on your point of view) The question was raised!! What about dual fuel Ranges ??
In this instance electrical isolation would fail to remove the source of ignition, (The gas hob would still be burning) In this instance ie dual fuel, the isolation would be even more suited to isolation for maintenance purposes.

The range in question is Dual Fuel, and as such I would deem the isolator code 4 my reason being the location is simply not correct.
Had the range been All electric then to cover myself on a pir I would feel justified in a code 2
My reasoning Dual fuel for isolation for maintenance purposes.
All electric Isolation for maintenance and emergency purposes.

As said the code 1 is a non starter. I am sorry that the answer is not definitive, I really was hoping to get something that would take away the personel opinion scenario that the thread as shown.
Despite long conversations with regulating bodies and informed individuals, its still left with us the sparkies to pick the wood from the trees because you will still get the greys come up, and not black and whites.
 
If after suitable risk assessment, an isolator for emergency switching is deemed necessary.
Such would also apply to the gas/oil part of the range, and could be achieved by the installation of a solinoid.
As for the code 4, again a specific Regulation would have to be breached, before any code is issued.
 
If after suitable risk assessment, an isolator for emergency switching is deemed necessary.
Such would also apply to the gas/oil part of the range, and could be achieved by the installation of a solinoid.
As for the code 4, again a specific Regulation would have to be breached, before any code is issued.

I would agree spin. The selenoid scenario with emergency gas shut off is widely used in commercial installs. Rarely if ever seen on domestic though. Most gas shut off systems are an integral part of the appliance when deemed neccassary.
I must say, getting informed advice on the subject, is a bit like asking a financial advisor about what you should do with a pension. They will advise you but will not commit to making the decision for you. It seems there isnt really a wrong or right answer on this one. You just have to look at all the facts, and come to your own conclusions. Bottom line is, being able to prove your decision was an informed one taking into account all the rellevent factors, and not based solely on a personal opinion.

Very many thanks to all contributing to this thread, and to the mods who run the sight.
It leaves all of us better informed in these days of trying to do the right thing, and keeping our standards up.
As for making a living when the guys with the horses ride off into the sunset with a wadd of cash regardless, Well !! Dont get me started on that one.
 
New posts

Reply to Range Oven Isolator Position Deemed Code 1 on a PIR ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how my oven is currently wired up, followed by 3...
Replies
0
Views
946
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi, I am not an electrician and looking for some electrical advice. We have had a new electric roller door installed at our warehouse. The door...
Replies
3
Views
2K
Hi all. Just finished a domestic EICR where I found the cooker isolator to be smack bang in the middle of the actual cooker position. The oven...
Replies
22
Views
3K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock