If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix
I need to do the customer a report on this. done buy a supposed "electrician" via Bathroom installers. This SWA is for a 9.5kW shower.

apart from the SWA armour not being earthed, the black core is used as cpc but no Gn/Y ID. joins in loftto T/E in a broken adaptable box with 30A 3 pole choc strip. the SWA is exposed in the CU room and drilled out through cavity wall, then takes a convoluted route up outside wall to attic. Apart from having 2 tight bends where it enters wall, it's a bloody eyesore. a minor point is the grey conductor is unused and I beleive it should be connected to earth.

They have at least fitted a 40 RCBO albeit a Wylex in an Ashley& Rock CU.

What i need is reg. nos. from 18th for above non-compliances if anyone could oblige, as I still only have 17th (3rd Amdt.)joannaCU.jpg
 
Last edited by a moderator:
I have a spare copy of 18th if you want it.
 
522.8.3 The radius of every bend in a wiring system shall be such that conductors or cables do not suffer damage and terminations are not stressed.
 
  • Like
Reactions: DPG
522.8.3 The radius of every bend in a wiring system shall be such that conductors or cables do not suffer damage and terminations are not stressed.
thanks for that
 
not got mine to hand but you are going to get a lot of reg numbers thrown at you by many I suspect.

reg 155.TH155.5H1T.4.RE4L
springs to mind??
 
  • Like
Reactions: ferg and 123
526.1 Every connection between conductors or between a conductor and other equipment shall provide durable electrical continuity and adequate mechanical strength and protection. Broken box and 30A choc block no good for that.
[automerge]1587036297[/automerge]
Most of section 134 Erection and Initial Verification.

134.1.1 Good workmanship by skilled or instructed person. Proper materials to be used in the errection of the electrical installation. The instalation shall take into account manufacturers' instructions.
 
Last edited:
Would also point out that as this installation was carried out by someone "at work" then the EAWR reg 8 should also come into it.
 
@ tel, just ping me your address or you can pick it up from Ashbourne, Derbyshire which i think is the closest place i work to you.
 
  • Like
Reactions: DPG and ruston
my draft report.
Report on Shower installation



!. SWA cable does not have the steel armour earthed.

2.The SWA is not adequately supported at the Consumer Unit ( 522.8.5 )

3. The black conductor used as cpc is not identified as such (Green/Yellow Sleeving or tape required)

4. The joint in the attic to Twin&Earth cable is inadequately joined with 30A connector blocks, as the circuit load is 41A. There is no strain relief provided. ( 526.1. & 522.6 )

5. The RCBO fitted is 40A. This is inadequate as it does not comply with Ib<In<Iz.

6. Where the SWA enters the structure, the bend radii are too tight ( Reg. 522.8.3 )

7. The SWA cleats outside are spaced too far apart ( Reg. 522.8.4. )

Section 134 of BS7671 applies.

It is my considered opinion that this installation is non-compliant; the SWA outside the building will allow water ingress into the masonry and is an eyesore.

My recommendation is to rip it out and start again.
 
  • Like
Reactions: DPG and ChipFanDave
514 for identifaction of conductors.
 
Armour not earthed, 411.3.1.1
Conductor identification, 514.3
Unsuitable connection enclosure, 526.7
Bends in swa cable, 522.8.3
Non compatible protective device, 536.4.203
There are multiple Regs you could throw at this including the slick termination of the cable at the board.
 
Armour not earthed, 411.3.1.1
Conductor identification, 514.3
Unsuitable connection enclosure, 526.7
Bends in swa cable, 522.8.3
Non compatible protective device, 536.4.203
There are multiple Regs you could throw at this including the slick termination of the cable at the board.
SUPER. THANK YOU.
 
I wouldn’t include no 5 in your report, as overloaded protection can be omitted for fixed loads such as a shower so ib<In<Iz is not relevant, you just need to make sure that the Iz of the cable is large enough including the protective device for the load of the shower and that you have the required fault protection.
So in this case the rcbo is incorrectly sized for the final load 433.1.1 (i)
 
Last edited by a moderator:
Apart from all that sounds like a good job.
 
  • Funny
Reactions: DPG
well, it doesa work. but can't for the life of me understand fitting an instantaneous shower when it would be far less work fitting a mixer shower, hot feed from C/H boiler. all the necessary pipework( not necessarily in the right order though) is under the floor only about 4 ft. away.
[automerge]1587049839[/automerge]
I wouldn’t include no 5 in your report, as overloaded protection can be omitted for fixed loads such as a shower so ib<In<Iz is not relevant, you just need to make sure that the Iz of the cable is large enough including the protective device for the load of the shower and that you have the required fault protection.
So in this case the rcbo is incorrectly sized for the final load 433.1.1 (i)
so i'm half right. the 40A MCB is running at above In, so is in danger of tripping if shower is used by teenage girls, which in this case, it is. 1 x 14 year old monster teenage daughter.
[automerge]1587049912[/automerge]
Apart from all that sounds like a good job.
just seen a pink pig in flight over the trees.
 
Last edited:
Seriously, WTF! Does the cover fit on that CU?
 
  • Funny
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
Supporter
~
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
Report.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Thread Tags

Advert

Thread statistics

Created
telectrix,
Last reply from
telectrix,
Replies
20
Views
2,149

Advert