i was asked to pull in a shower cable and leave in wall for future as customer has been roked into other work, so makes sense now as they have the room.

9.5kw shower on 6mm is fine according to osg upto 43m on ref method c. i only have an 8m run and is in rafters with kingspan but kingspan wont be touching it. it has 150mm rafter with only 100mm kingspan..
so at least a 50mm gap around cable
i said its dead on for 8.5kw shower but i do think 9,5 will be fine aswell.


thoughts
 
also when i do adiabatic and use 5 seconds im getting 41 ? why
 
If the cable is not in or under any insulation then 6mm should be OK for 9.5kW.
I get 3.88 with the adiabatic equation (for a 40A BS60898).
 
I'd be tempted to just put in 10mm cable then all is covered e.g wanting a 10.8kw shower in the future
 
well righard there is only a 2.5mm in the 6mm t&E
If the cable is not in or under any insulation then 6mm should be OK for 9.5kW.
I get 3.88 with the adiabatic equation (for a 40A BS60898).

- - - Updated - - -

200 x 200 for the 40A breaker
How do you get that without knowing the PFC of the circuit? :bucktooth:
 
Richard has used the Ia value for the breaker (200A) which would cause the breaker to operate in 0.1secs.

S = √(I² x t) ÷ k
S = √(200² x 0.1) ÷ 115 = 0.55

However the correct value to use is the actual fault current that could flow in the event of a fault (Ipf = Uo ÷ Zs) which could be a lot higher if the Zs is low enough.
 
Last edited by a moderator:
  • Like
Reactions: 2 people
Stick 10mm in and you will definitely be ok for the future. It may be a bit of a git to get into switch terms but it won't burn if it gets covered.
 
ive already put in 6mm as i knew this would run an 8,5kw and was 40 quid cheaper per 50m roll.
 
Tell em to use a 7.5KW shower if they need one. Good enough for my kids AND it saves water to boot....
 
Tell em to use a 7.5KW shower if they need one. Good enough for my kids AND it saves water to boot....

and what thhen do you do with the water in yer boot? :drummer:
 
mmm tadpole wellington. makes a change from beef.
 
still cant get me adibiatic right for this shower.. its a tn-c-s so say max of 0.35 ohms and its 10m max so say 0.45 as calculated zs = 511A

511 x 511 = 261121 x 5 = 1305605 / 115 =11353 and the square root off 11353 = 106 which is wrong.
 
Why do you think your protective device will take 5 seconds to operate?
 
well its over 32A
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
Supporter
~
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
shower on 6mm for future
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
i=p/u,
Last reply from
JUD,
Replies
28
Views
3,075

Advert