So this was an interesting conversation today and wanted peoples advice.

Plumber asked me if I could fit a socket inside an enSuite Vainty unit. I asked why and he said the customer had bought a japanese toilet (the ones with the air, water and lights ect)

Japanese toilet is off a cable with a built in RCD.

There is a socket in the room next door so I wanted to chase out, run the cable next door and wire a fused Spur off a socket to clear any issues with zones.

Plumber said the customer doesnt want that he wants a socket in the vanity unit and the cable for the toilet wiring to a plug. He thinks becuase its under a sink in a cupboard its classed as outside zone.

While it is outside zone the regs state "Electrical sockets are permitted in bathrooms or shower rooms as long as they are located more than 3m from the edge of the bath or shower. Specially designed shaver units are an exception to this rule and can be located slightly nearer, but still no closer than 600mm from the bath or shower."

Thoughts??
 
Lol, I am not sure if I would want to sit on a 230 volt toilet.
ITs this. I really dont get it but since telling the wife she now wants one.



Customer / Plumber (I think the plumber is using the customer to get his point accross) now saying the compromise would be a FCU in the vanity unit, imo thats still a no no (I know there are exceptions with FCU with rear cable entry) but for me If Im doing that Id rather just a normal FCU in the room next door as Im still chasing the wall out either way.
 
ITs this. I really dont get it but since telling the wife she now wants one.



Customer / Plumber (I think the plumber is using the customer to get his point accross) now saying the compromise would be a FCU in the vanity unit, imo thats still a no no (I know there are exceptions with FCU with rear cable entry) but for me If Im doing that Id rather just a normal FCU in the room next door as Im still chasing the wall out either way.
It does say in the instructions to be fitted with a 13 amp fused spur.
If you are not happy with the environment in terms of the compliance with the current regs then stick to your guns..
 
I remember being in Japan and finding the toilets at this new university building very strange. The high-tech seat had a control panel next to the throne with about 20 buttons, all with Japanese characters, so I had no idea what they would do. Rather ominously, one looked like a red emergency stop!

But in-spite of this fancy stuff, they seemed to have omitted any hand drying facilities. I saw someone had left a few paper towels, and I thought maybe it is work in progress, so next time I tried a toilet on the floor above where I was working. Exactly the same!

Edited to add: I decided not to experiment with my own bottom, and unfortunately there were no volunteers to find out what all those buttons did.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scunthorpe
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Socket inside a En Suite Vainty Unit???
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
Creamy Goodne5,
Last reply from
pc1966,
Replies
21
Views
5,608

Advert

Back
Top