IEC standard 60947-3 (same BSEN number) which covers switch disconnectors or isolators will tell you that they must be designed to withstand fault currents flowing through them until the protective device operates.

From what you have discribed there is no problem with the way the circuit has been installed.
 
Your thought, that the isolator is undersized @ 20A, is based on the fact that the protection is 32A

This is EXACTLY the same as saying the protection @32A is oversized as the isolator is only 20A

The regs only need to cover one point of view as the other is automatically covered!
Not really, the circuit supplies 2 split units each drawing around 12A so it has been designed as a 32A cct for that reason. I see what you're getting at but this has been designed as a 32A cct & is wired in 4mm singles. The isolators that have been fitted are there because of the availability of the correct parts in the location I'm in.
 
Not really, the circuit supplies 2 split units each drawing around 12A so it has been designed as a 32A cct for that reason. I see what you're getting at but this has been designed as a 32A cct & is wired in 4mm singles. The isolators that have been fitted are there because of the availability of the correct parts in the location I'm in.

OK, but your view is that the isolators are undersized @20A, based on the protection device of 32A. This is exactly the same as the protection device is oversized @ 32A compared to the 20A isolators as far as the regs are concerned; 432.3 details why this situation is permissible.

As long as it's a fixed load and it has fault protection, it is compliant

If these same isolators supplied multiple outlets, then it's not a fixed load and your point would be valid as someone could just plug in more loads resulting in overloaded isolators.
 
The what about 20AX switches on a ring final circuit with a 32 amp protective device? Millions of homes in the UK have this set up with no adverse effects.
 

Reply to Suitability of circuit accessories. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
266
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
196
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
789
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock