I have a 48” T8 fixture that I recently added LED’s by removing the ballast and wiring directly. After doing so when hanging the fixture with the chain, after plugging it in to turn it on I got a small shock from the chain.

Full disclosure, I do have some maintenance/electric experience, I worked maintenance for three years but had pretty limited exposure to electrical work; ie: changing ballasts replacing light fixtures etc.

I pulled it apart to see if I had any frayed wires or bad connections and didn’t see any obvious problems. I posted some pictures of how it’s wired and some damage to the connection (not sure if that’s shorting it or not.)

Any advice on where to start my diagnosis would be greatly appreciated!

*Let me know if any additional info/pictures are needed.
 

Attachments

  • IMG_6157.jpeg
    IMG_6157.jpeg
    349.4 KB · Views: 18
  • IMG_6156.jpeg
    IMG_6156.jpeg
    280.9 KB · Views: 18
Info: Located in US

I have a 48” T8 fixture that I recently added LED’s by removing the ballast and wiring directly. After doing so when hanging the fixture with the chain, after plugging it in to turn it on I got a small shock from the chain.

Full disclosure, I do have some maintenance/electric experience, I worked maintenance for three years but had pretty limited exposure to electrical work; ie: changing ballasts replacing light fixtures etc.

I pulled it apart to see if I had any frayed wires or bad connections and didn’t see any obvious problems. I posted some pictures of how it’s wired and some damage to the connection (not sure if that’s shorting it or not.)

Any advice on where to start my diagnosis would be greatly appreciated!

*Let me know if any additional info/pictures are needed.
 
There is obvious damage to the end cap.
Looks like it has either degraded with heat over time, or has been dropped?
 
  • Agree
Reactions: DPG
There is obvious damage to the end cap.
Looks like it has either degraded with heat over time, or has been dropped?
Honestly it was something I got for free and figured it wouldn’t be too much to fix. I’ll probably just replace that outlet and then test it.
There is obvious damage to the end cap.
Looks like it has either degraded with heat over time, or has been dropped?
 
Info: Located in US

I have a 48” T8 fixture that I recently added LED’s by removing the ballast and wiring directly. After doing so when hanging the fixture with the chain, after plugging it in to turn it on I got a small shock from the chain.

Full disclosure, I do have some maintenance/electric experience, I worked maintenance for three years but had pretty limited exposure to electrical work; ie: changing ballasts replacing light fixtures etc.

I pulled it apart to see if I had any frayed wires or bad connections and didn’t see any obvious problems. I posted some pictures of how it’s wired and some damage to the connection (not sure if that’s shorting it or not.)

Any advice on where to start my diagnosis would be greatly appreciated!

*Let me know if any additional info/pictures are needed.
I have to agree with @James on the broken fitting on the end of the bulb. It’s grounded properly but something is wrong because the chain shouldn’t have shocked you. Have you tried to check the voltage on the chain.
 
I have to agree with @James on the broken fitting on the end of the bulb. It’s grounded properly but something is wrong because the chain shouldn’t have shocked you. Have you tried to check the voltage on the chain.
The voltage on the chain is just under 5v
 
  • Like
Reactions: James
Could there possibly be wrong somewhere else ?
Not that I can see, I’m about to order some new lamp holders for it and see if that broken one was making contact with the housing. No bad wires visible all wire nuts are secure ect.
 
Not that I can see, I’m about to order some new lamp holders for it and see if that broken one was making contact with the housing. No bad wires visible all wire nuts are secure ect.
If possible keep us updated and good luck
 
  • Like
Reactions: DPG and dfunk93

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Minnesota, USA
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
T8 Fixture Hot, Ground or Short issue?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
dfunk93,
Last reply from
Megawatt,
Replies
8
Views
1,329

Advert