I'm an not that familiar with TNCS systems at all, as almost every system I work on is TNS. My question is this, is there a way to tell if a system is in fact a TNCS system. There is one I am currently working on which is labelled as PME, but rather that taking it as gospel that this means it is a TNCS are there any visual tell-tale signs, as I don't want to connect the earth to neutral if it is a TNS.

Thanks in advance.
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

refer to earthing diagrams in on site guide or mant other electrical books
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Why would you be connecting the earth to neutral anyway?
 
  • Like
Reactions: 2 people
Re: They say there are no stupid questions but I might be about to disprove that - PM

I'm an not that familiar with TNCS systems at all, as almost every system I work on is TNS. My question is this, is there a way to tell if a system is in fact a TNCS system. There is one I am currently working on which is labelled as PME, but rather that taking it as gospel that this means it is a TNCS are there any visual tell-tale signs, as I don't want to connect the earth to neutral if it is a TNS.

Thanks in advance.
with TN-C-S...both prospective short circuit current (PSCC)....and prospective earth fault current (PEFC) should be largely the same....

- - - Updated - - -

dont forget a TN-C-S uses the neutral as the earth path....
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

niceic snags and solutions earthing and bonding book all you need to no about earthing arrangements
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

If it's PME he would.
I always thought the neutral and earth should only be connected on the DNO side and only the DNO should be connecting them.
 
  • Like
Reactions: 3 people
Re: They say there are no stupid questions but I might be about to disprove that - PM

I always thought the neutral and earth should only be connected on the DNO side and only the DNO should be connecting them.
yes...otherwise you would have a TN-C system.....not allowed in the uk....
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Glen to pick up on two points

Firstly PSC is 27a and PFC is 1483 a. Would this make you wary that PME label is incorrect?

Assuming it is a PME system (TNC-S) should I be getting the DNO to connect the earth.

Thanks

yes...otherwise you would have a TN-C system.....not allowed in the uk....
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

glen to pick up on two points

firstly psc is 27a and pfc is 1483 a. Would this make you wary that pme label is incorrect?

Assuming it is a pme system (tnc-s) should i be getting the dno to connect the earth.

Thanks
pscc=27a????

- - - Updated - - -

whats your Ze?
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Yes, 27a as PSC and 1483 as PFC.

ZS - is 8.59 ohms. Which is high and a fail I know, under anything other than a TT, which it isn't. (Yet anyway). Currently arrangement is that what probably a PME system which has never had main earth connected to it, and instead is clamped to metal piping surrounding the incoming supply conductors.

I might redo PSC tomorrow to be sure.


With regards to above, would you believe the PME label? And if so, would you connect the earth or request DNO to do it?
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

first check your readings. then call DNO .
 
  • Like
Reactions: 1 person
Re: They say there are no stupid questions but I might be about to disprove that - PM

you cant make any assumptions on values like that Ken....as Tel here....
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Last thing, and I really appreciated the advice - in any case is always the DNO responsibiliy to connect earth to PME system.

Thanks again.

Ken
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

whats this about connecting earthing up to DNO equipment Ken?.....
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Last thing, and I really appreciated the advice - in any case is always the DNO responsibiliy to connect earth to PME system.

Thanks again.

Ken
yes it is...
 
Re: They say there are no stupid questions but I might be about to disprove that - PM

Cheers, thanks alot.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
They say there are no stupid questions but I might be about to disprove that - PME
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Ken77,
Last reply from
Ken77,
Replies
16
Views
1,854

Advert