Problems:
You say that:
<Resistance> Will be lower when calculated with armour.
But according to this manufacturers tables the resistance of the armour (8.8 ohms/km) is a higher than the 2.5 copper(7.41ohms/km). how does this affect your calcs?
Exported earth TN-S:
The armour is too small to for the earthing requirements at the garage end?
Any thoughts
many thanks for this.
Regads
Steve
best regards
Steve
Appendix 4 - Cable Data-Resistance, Impedance and []R1 + R2? Values - Guide to the Wiring Regulations - Locke - Wiley Online Library
Hi Steve
The actual CSA of the steel for 2.5mm SWA is 17mm, minimum CSA required as per table 54.7 is 5.7mm.
It's more for disconnection times really! The max zs at 80% for a bs3036 is 1.944ohms. Your actual is more on the lines of 1.603 (best to test Zdb at the garage).
Cheers