Thanks for this TD , very useful.
Problems:
You say that:
<Resistance> Will be lower when calculated with armour.
But according to this manufacturers tables the resistance of the armour (8.8 ohms/km) is a higher than the 2.5 copper(7.41ohms/km). how does this affect your calcs?

Exported earth TN-S:
The armour is too small to for the earthing requirements at the garage end?

Any thoughts
many thanks for this.
Regads
Steve


best regards
Steve


Appendix 4 - Cable Data-Resistance, Impedance and []R1 + R2? Values - Guide to the Wiring Regulations - Locke - Wiley Online Library

Hi Steve

The actual CSA of the steel for 2.5mm SWA is 17mm, minimum CSA required as per table 54.7 is 5.7mm.

It's more for disconnection times really! The max zs at 80% for a bs3036 is 1.944ohms. Your actual is more on the lines of 1.603 (best to test Zdb at the garage).

Cheers


Cheers
 
Many thanks TD. I didnt realise that it doesnt matter if its steel or copper. I thought the CSA was a representation of the resistance/km.. If it is then obviously the material is relevant.
I'm installing a new CU. I'm thinking of putting the garage on a timed RCD in the house to a garage box with a std RCD a 6a and 16a MCB.
Thanks again.
S
 
Many thanks TD. I didnt realise that it doesnt matter if its steel or copper. I thought the CSA was a representation of the resistance/km.. If it is then obviously the material is relevant.
I'm installing a new CU. I'm thinking of putting the garage on a timed RCD in the house to a garage box with a std RCD a 6a and 16a MCB.
Thanks again.
S


a what?
 
Many thanks TD. I didnt realise that it doesnt matter if its steel or copper. I thought the CSA was a representation of the resistance/km.. If it is then obviously the material is relevant.
I'm installing a new CU. I'm thinking of putting the garage on a timed RCD in the house to a garage box with a std RCD a 6a and 16a MCB.
Thanks again.
S

It does matter what material it is made of, and you use the relevant K factors to calculate for different materials.

Why does it need a time delayed RCD?
 

Reply to undersized SWA to garage code? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock