Hi guys,

i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )

It is a TT system with earth rod.

My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.

All the R1 + R2 and insulation resistance came back normal.

When I carried out the ZS tests, the reading were very high, for example:

Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !

same for lounge and bedroom rings.

I have checked to regs and these figures are over the maximum allowed.


Any advice ???
 
if your R1+R2 readings came back as satisfactory then that circuit impedance should be OK. Therefore you need to start looking at other factors relating to this issue i.e your Ze!! Are you earthing conductors connected correctly and secure and in good condition?

Get another rod sank in and see if this is any better to lower your Ze
 
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

??


Ok then your maximum allowed Zs reading for each 30mA protected circuit is 1667 Ohms, problem solved in 31 posts.

Your RCD at the supply end should ideally be an 'S' type time delayed to achieve discrimination with the RCD at the remote end but I wouldn't loose sleep over that one.
 
ZE reading 187ohm

I can determine ZS by enquiry, ZE +R1 +R2 = ZS

However, i tried to test and measure ZS at the end of the circuit and got these high figures of 2.6 2.5 etc etc...

again, any ideas on how to solve this issue???

Thanks

ok, first it's not an issue.

When you tested Ze, You disconnected the earthing conductor which went to the earth rod I imagine.

As previosuly mentioned, you may well have bonding in place to the Water service???

Try testing with the earthing conductor re-connected, and you will probibly get a reading of somewhere around 2 ohms. As previsouly stated by telerix, by connecting the water pipe you've effectivly got a much better earth rod!

With regards to the values in the Regs - Being a TT system, because your Ze is not garenteed stable, circuits must be protected via RCD (in your case 30ma), which from what you say they already are.
 
Last edited by a moderator:
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

would that be a 30mA RCD protecting the sub main and another 30mA RCD protecting the final circuits in the outbuilding i.e. 2 RCD's in series

I was too slow in replying to specialist (too slow, specialist beat me) sorry to cause confusion
 
Last edited:
ZE was 187

the system is protected by a 30ma RCD from the main house, and the new board is also protected by a 30 ma RCD.

would that be a 30mA RCD protecting the sub main and another 30mA RCD protecting the final circuits in the outbuilding i.e. 2 RCD's in series

too slow, specialist beat me

Hey: I've got to beat someone at posting at least once a year:lol:
 
sorry if i read that wrong mechelec but why would 2 rcd`s in series slow the disconnection time

It wouldn't "slow the discrimination time? " but it would mean there was no discrimination between the RCD's and it would be pot luck which would trip first. inconvenient at best, dangerous at its worst. First one should be time delayed or S type
 
So to confirm,

ZS readings of 2.6 ohms or there abouts is acceptable, providing the system and all circuits are protected by a 30ma RCD. (which they are)

??


Ok then your maximum allowed Zs reading for each 30mA protected circuit is 1667 Ohms, problem solved in 31 posts.

Your RCD at the supply end should ideally be an 'S' type time delayed to achieve discrimination with the RCD at the remote end but I wouldn't loose sleep over that one.
 
i got confused earlier, because a member said the my ZS reading could never be lower than my ZE...

My ZS of 2.6 etc is lower than 187 omhs.....?

So to confirm,

ZS readings of 2.6 ohms or there abouts is acceptable, providing the system and all circuits are protected by a 30ma RCD. (which they are)

??
 
It wouldn't "slow the discrimination time? " but it would mean there was no discrimination between the RCD's and it would be pot luck which would trip first. inconvenient at best, dangerous at its worst. First one should be time delayed or S type
yeah well this one cropped up here a while back......2 RCDs..both 30mA...both in series...one feeds the house..the other the garage/outbuilding...theres a fault in the garage/outbuilding...which lets go first?...
 
Last edited by a moderator:
i got confused earlier, because a member said the my ZS reading could never be lower than my ZE...

My ZS of 2.6 etc is lower than 187 omhs.....?

It's often lower because of parallel paths from bonding conductors etc. I explained in post 4.

Your 187 Ohms is Ra NOT Ze on a TT system, this is all in the On-Site Guide that you already mentioned, PLEASE read it thoroughly, there are large gaps in your knowledge and someone could be hurt because of this!
 
It's often lower because of parallel paths from bonding conductors etc. I explained in post 4.

Your 187 Ohms is Ra NOT Ze on a TT system, this is all in the On-Site Guide that you already mentioned, PLEASE read it thoroughly, there are large gaps in your knowledge and someone could be hurt because of this!

In mine too nowadays which I'm blaming on Alzheimer's. :(
 
You're scaring me Eng54. :aureola: This isn't some kinda new years resolution is it?


Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
 
Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
how about a lovely gas pipe..lol....
 
just to confirm, I never said I was satified with my high RA, just giving the facts and hope to get good information from the forum.

I will be looking to lower the RA, however it is deemed as ok according to the Regs..


Not really, just that there are more than enough posters on this thread already!! lol!!

Does seem strange though, that the OP is more than satisfied with his Ra of 185 ohms or whatever, ...and for his own house!! Seems he didn't even give a thought to adding a couple of rods at the workshop end, or adding on a rod, at the existing rod for the house.... Oh well, his house and his family!!! lol!!!
 

Reply to Very Hi ZS Reading on TT system? any advice in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock