Discuss Voltage still detected after rcd had tripped? why could this be... in the UK Electrical Forum area at ElectriciansForums.net
S
srl-8
Hi all,
I have install a RCD fused spur on the end of line feed to a bathroom lighting circuit. Thus protecting the bathroom with rcd.
I tested the rcd (manually via the push 'test' button) and it killed the lights and fan as expected.
I used my volt stick to confirm that the cables were dead, but to my surprise , The voltstick was telling me the there was voltage still present. How could this be?
My understanding was that with the RCD tripped, it should kill all power on the load side of the spur, .
Any ideas????
voltstick picking up off incoming side. use a proper tester to confirm. voltsticks are only a rough guide and don't bloody rely on them.
Use a multimeter/ MFT rather than a voltstick to confirm what voltage is where. Voltsticks are useful but only give an indication and can be easily confused by capacitive coupling / induced voltages.
E: and again we have proof that great minds think alike, although Tel types faster
Yes, I agree that voltstick is not a 100% guarantee, I will test what voltage is present when I go back to finish the job, just had never noticed this before.
Cable bunching can confuse a voltstick, however, the RCD (to my understanding) should break the power on both live and neutral. So there should be no current available to detect on the load side of the spur and bathroom circuits.
No current, indeed. But a voltstick detects... voltage. And a small amount of leakage or coupling from a live cable can cause the isolated circuit lives to float up to a voltage that the stick can detect. Readings needed.
You need to use the proper test equipment voltsticks have their uses but NOT to prove dead or live
Hi all,
Any ideas????
What voltage was your MFT showing at a load point after you'd tripped the RCD?
New posts
Reply to Voltage still detected after rcd had tripped? why could this be... in the UK Electrical Forum area at ElectriciansForums.net
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...