Hi all,

I have install a RCD fused spur on the end of line feed to a bathroom lighting circuit. Thus protecting the bathroom with rcd.

I tested the rcd (manually via the push 'test' button) and it killed the lights and fan as expected.

I used my volt stick to confirm that the cables were dead, but to my surprise , The voltstick was telling me the there was voltage still present. How could this be?

My understanding was that with the RCD tripped, it should kill all power on the load side of the spur, .

Any ideas????

Thanks
 
voltstick picking up off incoming side. use a proper tester to confirm. voltsticks are only a rough guide and don't bloody rely on them.
 
Use a multimeter/ MFT rather than a voltstick to confirm what voltage is where. Voltsticks are useful but only give an indication and can be easily confused by capacitive coupling / induced voltages.

E: and again we have proof that great minds think alike, although Tel types faster
 
Yes, I agree that voltstick is not a 100% guarantee, I will test what voltage is present when I go back to finish the job, just had never noticed this before.

Cable bunching can confuse a voltstick, however, the RCD (to my understanding) should break the power on both live and neutral. So there should be no current available to detect on the load side of the spur and bathroom circuits.
 
no current available to detect on the load side of the spur
No current, indeed. But a voltstick detects... voltage. And a small amount of leakage or coupling from a live cable can cause the isolated circuit lives to float up to a voltage that the stick can detect. Readings needed.
 
You need to use the proper test equipment voltsticks have their uses but NOT to prove dead or live
 
Hi all,

I have install a RCD fused spur on the end of line feed to a bathroom lighting circuit. Thus protecting the bathroom with rcd.

I tested the rcd (manually via the push 'test' button) and it killed the lights and fan as expected.

I used my volt stick to confirm that the cables were dead, but to my surprise , The voltstick was telling me the there was voltage still present. How could this be?

My understanding was that with the RCD tripped, it should kill all power on the load side of the spur, .

Any ideas????

Thanks

What voltage was your MFT showing at a load point after you'd tripped the RCD?
 
Use a multimeter/ MFT rather than a voltstick to confirm what voltage is where. Voltsticks are useful but only give an indication and can be easily confused by capacitive coupling / induced voltages.

E: and again we have proof that great minds think alike, although Tel types faster
i like to think they show potential, potential to injure yourself or generally make yourself look like a --- waving a stick with a flashing red beacon like some crazed harry potter fan
 
All,

I have to say, (with a few exceptions) you come across as a **** taking bunch of smart arses. You all use volt sticks, you are telling lies if you say you don't. I never said that I rely on this method to confirm voltage. It was an observation and wanted to ask other people.

With-in a few replys this forum has 'Assumed' I don't know what im doing.

I future I will think twice before I post. Ouch!

PS: Many thanks to those who offered sensible responses.
 
All,

I have to say, (with a few exceptions) you come across as a **** taking bunch of smart arses. You all use volt sticks, you are telling lies if you say you don't. I never said that I rely on this method to confirm voltage. It was an observation and wanted to ask other people.

With-in a few replys this forum has 'Assumed' I don't know what im doing.

I future I will think twice before I post. Ouch!

PS: Many thanks to those who offered sensible responses.

In which case you should use the "thanks" button so we can see which ones you appreciate!
 
All,

I have to say, (with a few exceptions) you come across as a **** taking bunch of smart arses. You all use volt sticks, you are telling lies if you say you don't. I never said that I rely on this method to confirm voltage. It was an observation and wanted to ask other people.

With-in a few replys this forum has 'Assumed' I don't know what im doing.

I future I will think twice before I post. Ouch!

PS: Many thanks to those who offered sensible responses.

I'm not lying, I definitely don't use them. I have used voltsticks in the past, but in my experience they give false readings either live when dead or vice versa.
If I had used one and got a spurious reading however, my first thought would be to prove with my AVI what was going on, not ask an internet forum. That would give the impression I don't know what I'm doing or have the right tools for the job. I think that is what you have got stick for.
 
Quick few games to show voltsticks pick up stray and non dangerous currents.... place voltstick near tv screen... rub voltsick on your jumper, all will lite the voltstick, but non are dangerous.
 
Yes, I agree that voltstick is not a 100% guarantee, I will test what voltage is present when I go back to finish the job, just had never noticed this before.
Cable bunching can confuse a voltstick,
however, the RCD (to my understanding) should break the power on both live and neutral. So there should be no current available to detect on the load side of the spur and bathroom circuits.
This can be overcome by using your finger on the end of the voltstick and slightly separating the cables as you scan.
I use a voltstick on a regular basis and it has served me well over the years in fact I would go as far as saying that it's potentially saved my life on at least a couple of occasions when I unwittingly came across a 'borrowed' neutral, that's after safe isolation was carried out, all appeared okay until I split the neutrals and one magically became live! They're also great for detecting broken neutrals in extensions.
 

Reply to Voltage still detected after rcd had tripped? why could this be... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
557
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
539
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock