Tested an RCD today, 30mA.
15mA time : >1999ms
30mA : 44.1ms on 0degrees / 53.8 on 180degrees
150mA : 15.8 on 0degrees / >40ms on 180degrees.
I did this four times, similar results each time. Zs at that socket 0.91ohms.
I don't understand why an RCD would trip on one angle of the phase and not the other.
Can anyone fill me in?
Thanks in advance