I'm not sure where you are getting 80% after 15 years from as all panel manufacturers have performance at 80% after 25 years so 0.8% reduction per year. A panel manufacturer (say solar world) who have 0.7% guarantee per year would mean a system producing 3600 kWh in year one would produce 3,040 kWh after 25 years at 0.7% reduction and about 2940 kWh at 0.8% reduction after 20 years.
You'll make about 100 kWh more per year using a Steca Grid inverter. Stuff like high temperature and low light performance of panels are just if not more important than 25 year performance warranty guarantees