I'm after a crabtree starbreaker D6 MCB.... any ideas please ? Tried a few wholesalers that I use with no joy
Cheers Sy
Not sure whats going on with the title of my post - "Dont you just love RCDs!!" (was a previous posts title) Should read "Crabtree Starbreaker MCB"
Reactions: 1 person
Thanks Mogga no joy there just B or C... starting to have my doubts wether they actually made a 'D' Type ?
theres a place in ballamena , n.ireland called flouresnt plus who gather up all old breakers, you could try them ive only used them once and it was a fiver which earned me a 100 Fluorescents Plus
Cheers Sy
Crabtree don't do a Type D MCB for their domestic Starbreaker or Loadstar boards. Only Types B and C available.
Yeah Just seen that on there website, great...... right plan B
This is going to work out to be an expensive light fitting for my customer.
Basically he's brought some fancy fitting with a transformer in it, which keeps tripping the MCB - he's read the fitting instructions further and it states requires a type 'D' mcb. Thats a new one for me.
So now looks like I'm going to have to split tails a separate mini cu just to do re-do the lights on a 'D' :dizzy2:
But haven't seen many 'D' types for domestic CU's ???
Any thoughts ?
just out of interest as well......whats the length of run from the origin of supply to the last point on this circuit?....
Ummm off the top of head... guess-timate would be 30-50 meters (large 5 bed house / down stairs lighting circuit)
Whys that then, what you thinking ?
max. Zs on a type D is about 1.5 ohms.. iv'e got a couple of starbreakers, think thy're type B though. why do you want a type D for lighting?
Glenn,
Why would he have to watch his Zs ?, surely this circuit would still have to have 30mA RCD protection if he is making changes to the OCPD ?
BTW Iam aware of the lower Zs required for D type MCB's.
Just asking
Glenn,
Just asking
well do you think it prudent to rely on an RCD alone?....like a TT system?.....thats whats being advocated here.....
Not at all,
he is going to be no where near the much criticised magic 200 ohm (1667 ohm) number though is he ?
Not at all,
he is going to be no where near the much criticised magic 200 ohm number though is he ?
the thing here as well is short circuit...i just dont like the idea of relying on additional protection alone on the basis of using a d type when a c type would probably hold........
A 6A B type or D type is still 6A regardless, only the max Zs has changed for the disconnection time, if it complied for a B-type before then it still complies now in this respect (Short circuit).
if his Zs is say 2 ohms (for instance) then his 30mA RCD will mitigate this, not rely soley on RCD protection.