EICR today on a holiday cottage.
Suffice to say they’ve agreed to a board change along with some other remedials.
I took the cover off…. That’s not one of the faults… but straight away missing busbar shield, mismatched devices no RCDs whatsoever and 1.5mm cable spurred off a 32A mcb.