andrew8902

Hi. I found a radial power circuit on an EICR yesterday wired in 6mm2 flat twin PVC cable and have some concerns. I know that the MCB is designed to protect the cable but what about the terminals of the sockets? 13A socket-outlets are rated to 20A max and I am not sure they are designed to have 2 x 6mm2 conductors in the terminals? I thought they were designed for 3 x 2.5mm2?
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks
 
MK technical permit 2×6.0 stranded conductors and 3×4.0 stranded. What is the reference method for the cable.
 
  • Like
Reactions: Deleted account
The 20A limit (I think) you mention is for the load on a double socket, not the through-current on the terminals.

The basic principle behind 13A plugs and sockets is they have the protective fuse, so it does not matter (within reason) what the supply is, so long as the supply cable is protected. After all cooker switch/outlets often have up to 45A MCB feeds.
 
It's unlikely that any current from other sockets is passing through the socket terminal, it's passing through conductors which are touching each other and touching the terminal as well.
 
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks
Would be limited by 13A fuse in plug, or 26 between two, as any other wiring method.

Not worth a code, but maybe a note.
 
Unconventional, but nothing wrong regs wise.
 
  • Like
Reactions: DPG
Depends on the reference method for the cable.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
13A BS1363 socket-outlets on a 40A MCB
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Tags Tags
mcb

Advert

Thread statistics

Created
andrew8902,
Last reply from
westward10,
Replies
7
Views
6,128

Advert