Hi all

doing a job in a modular portacabin, there are 6 different modules and are all bolted together to create 1 building. Each module has its own consumer unit which has 3 sockets and 1 lighting circuit and each one having its own mcb for each point. Therefore having 4 mcbs. The thing is i need to fit a heater in each module and i was wondering if it would be ok to spur off one of the sockets for the heater or do i need a designated supply.... Hope this makes sense

regard
gary
 
Makes sense Gary, No problem with supplying a 2kW heater via a FCU spurring off one of the sockets. When you mentioned there was 4 MCB's in the CU was that one MCB per socket outlet?
 
makes sense gary, no problem with supplying a 2kw heater via a fcu spurring off one of the sockets. When you mentioned there was 4 mcb's in the cu was that one mcb per socket outlet?

hi

ye one mcb for each socket , i always thought anything that was 2kw and above should have its own supply. To be honest it will be much easier if i could spur off the existing.

Regards
gary
 
Thats fine Gary:).

The reg you're thinking of concerns ring circuits and overloading of them at one point by connecting appliances rated at 2KW or greater to the them, this where it sates they should have their own circuit.
 
If there were say 2 heaters then would you put in a new circuit or add another spur. Only reason I ask is at the minute I'm helping out a friend and he's stuck 2 2.4kw plinth heaters both as spurs of a 20 amp radial.

Personally I would of ran a new radial and added the 2 FCUs to the readial instaed of coming off the socket radial circuit.
 
Hi mate,

one radial for each appliance over 2Kw, so you will be needing 2 new radials 2.5mm T&E, I usually fit a 16a breaker, but a 20 is acceptable as well.;)

Cheers.......Howard
 

Reply to 2 kw heaters in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the...
Replies
3
Views
1K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
743
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock