I saw an oven that was rated at 3,100 watts. Now most would say that cannot be fitted on final ring circuit as rule of thumb. But:
3,100 watts draws amps of:
14.09 amps @ 220v
13.47 amps @ 230v
12.91 amps @ 240v
12.4 amps @ 250v

If the installation is 240v or 250v then it safely inside the 13 amp of a final ring circuit.

The question is, and the regs aficionados can help here, what is the voltage that should be used to assess, as maybe the voltage will vary in an installation over the years.
 
It should be calculated at its rated voltage and power.

At higher voltages it will pass MORE current not less, and lower current at lower voltage.
So what you are saying, if say it is 250v, as mine is, this 3.1kW oven is OK to fit on a final ring circuit as it draws a maximum of 12.4 amps. My concern is that if the supply voltage drops in a few years for whatever reason, the current draw is too large blowing the 13A fuse. So is there a set voltage that is used for these calcs, like say 230v?
 
Last edited:
all depends on what voltage the manufacturer has used to specify the kW rating.
say he's used 240V, then I= 3100/240 = 12.916 A.
from above you can wirk out the resistance of the cooker. R = V/I = 18.58 ohms.

using the above reisistance at 220V:

I = V/R = 220/18.58 = 11.84A which equates to 2.604kW,
 
So what you are saying, if say it is 250v, as mine is, this 3.1kW oven is OK to fit on a final ring circuit. My concern is that if the supply voltage drops in a few years for whatever reason, the current draw is too large blowing the 13A fuse. So is there a voltage that should be used for these calcs, like say 230v?
It depends on the figures, say the rated voltage and power is 230V, 3100W

Then the resistance will be around 17ohms (V^2/P) so

220V =220/17 = 13A
230V =230/17 = 13.5A
...
250V =250/17 = 14.7A

There are two answers of course - this would be the sustained current - that current it would take to heat up.

And the average current - which would over a very long time (cooking the turkey for example) where the current switches on and off to maintain the temperature, but you can't use this to cable size.
 
X post, same principle, different choice of rating!!!

Great minds and all that.


Tbh though just squeezing it to be acceptable does not a good job make.
 
Tbh though just squeezing it to be acceptable does not a good job make.
I agree. A border liner. It may be fine then the voltage changes then problems, so best be on the side of caution.

I noticed a number of Continental appliances that are 3.1 kW, so wanted to know if there is a set voltage for these calcs for borderline appliances, irrespective of what voltage is supplied to the premises.

A place I had at one time had the voltage dropped from 240v to 230v over a few years, so relying on what is there now is not a good approach.
 
So what you are saying, if say it is 250v, as mine is, this 3.1kW oven is OK to fit on a final ring circuit as it draws a maximum of 12.4 amps. My concern is that if the supply voltage drops in a few years for whatever reason, the current draw is too large blowing the 13A fuse. So is there a set voltage that is used for these calcs, like say 230v?

But if the supply voltage drops, then the current drops. So there is less chance of the supply fuse blowing.
 
With you mentioning a 13A fuse blowing, are you suggesting putting it on a plug top? I never like running anything close to 13A on a plug top as have seen examples in the past of this causing the plugtop to melt.

If you're suggesting adding a spur into a ring main, isn't there something in Appendix 15 about any heating appliances 2kW and above having to be on a dedicated circuit?

Ps. I'm not a regs expert nor do I do domestic work so could be wrong.
 
I agree. A border liner. It may be fine then the voltage changes then problems, so best be on the side of caution.

I noticed a number of Continental appliances that are 3.1 kW, so wanted to know if there is a set voltage for these calcs for borderline appliances, irrespective of what voltage is supplied to the premises.

A place I had at one time had the voltage dropped from 240v to 230v over a few years, so relying on what is there now is not a good approach.
Agree, but I think you are still misunderstanding the relationship, if the voltage drops, so does the current, the real issue is if the voltage increases
 
It's important to remember that different loads behave completely differently when the voltage decreases.

Resistive loads e.g. heating elements: Current decreases proportionately with voltage, power decreases as square of voltage. If under thermostatic control, duty cycle increases inversely to square of voltage to maintain constant average power.

Tungsten lamp loads: Current decreases but not linearly and not by much over the usable range of brightness, because positive temperature coefficient of resistance of filament partially compensates.

Linear PSUs (somewhat obsolete): Current remains approximately constant, power decreases, efficiency increases until output falls out of regulation.

Switched-mode PSUs, LED drivers etc: Current increases in inverse proportion to voltage, to maintain approximately constant power input.

Induction motors: Current increases, PF typically increases, the relationship depends on load, motor design etc.

Returning to the subject of the cooking appliance. If the power rating is given at 230V it will take rated current at 230V and more at 240V. If the power rating is given at 240V it will take rated current at 240V and less at 230V. Many heating elements only deliver rated power at their highest rated voltage, making that the worst case for current.
 
Returning to the subject of the cooking appliance. If the power rating is given at 230V it will take rated current at 230V and more at 240V. If the power rating is given at 240V it will take rated current at 240V and less at 230V. Many heating elements only deliver rated power at their highest rated voltage, making that the worst case for current.
I think I have an answer. It is rated 220-230v. A rating of 220v, find resistance then apply that resistance to a 230v supply to get worse case of those two voltages.
 
New posts

Reply to 220v. 230v, 240v, 250v? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having replaced a single socket with a double and added a second double in the same room by extending the ring, by chance I found that there was...
Replies
17
Views
2K
S
Hi there I'm working in a pizza take away doing the installation for it . Just recieved The kitchen appliances rundown and now planning my final...
Replies
8
Views
6K
Specialist
S
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
P
Evening chaps. Long time reader first time poster right here, big fans of your work and all and I'm hoping to call upon your collective experience...
Replies
12
Views
2K
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
Replies
1
Views
2K
sxsparky
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock