hi just to check my sums are correct I will be running my oven of a 60 amp 3 phase breaker as the oven draws 51 amps I will be using a 5 core 10mm swa lsf cable to a 63 amp commando skt outlet does any one have any issues that may have missed any advice welcome
 
Looks OK to me, provided that any cable derating factors have been taken into account and your volt drop is OK.
 
I concur Handy :)
 
  • Like
Reactions: 1 person
Why would you be fitting a commando socket to a ''fixed'' industrial oven??

Why not a local / adjacent 3 phase and neutral 63A isolator??
 
Last edited by a moderator:
engineer 54 its being provided with a 63 amp commando socket

I dislike heavy power fixed equipment being permanently supplied via plugs and sockets. The amount of times, when it comes to pulling the plug out, maybe or maybe not after many years of service, you find it's welded itself to the socket!!


None of our fixed kitchen equipment is supplied via plug and socket, all are connected to IP rated fixed switch isolators.
 
  • Like
Reactions: 2 people
I see your point but as far as ive been told it will be supplied with the 63 amp plug attached and may well void the warranty have you looked at the rest of the sums just for my peace of mind
 
Please don't go there on a warranty issue, heard it all before, that is just pure scaremongering!! Any approved means of connection to a fixed supply (eg, switch fuse / switch isolator /plug & socket etc) that is recognised by BS7671 and you won't VOID any warranty. Double indemnity if the person making the connection to the supply is a qualified electrician!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
37 kw industrial oven
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
melvinmoo,
Last reply from
Engineer54,
Replies
15
Views
6,124

Advert