Not got my reqs or on site guide with me today could some one explain or show me an example to work out earth size 230v supply ze = 0.12 customer been told about calculation rather than need to upgrade earth system and i cant remember formula or how to do it thanks in advance lads
 
I = 230/0.12 = 1.92kA.

S= sq.rt. ( Isq. x 0.1 ) /143.
 
Last edited:
telectrix thanks for help but how would i calculate what size earth cable to use for installation by the above formula not done this before allways put in 16mm main earth 10mm water and gas thanks
 
  • Like
Reactions: 1 person
Minimum earth size using the formula and values tel has given from you readings is 4.24mm2 anything above that and you can assume adequate but if fitting would need to be subject to minimum size for earthing system.
 
richard thanks for advise but coukld you explain step by step how you got that if you dont no ask always been my policy once ive been shown will store in my human hard drive many thanks
 
this is how I did itadiabatic.jpg
 
there is no set values for main earth, just main protective bonding, minimum 6mm for tns,tt and minimum for tnc-s 10mm,

the valuers are in the book if you cant be bothered too count
 
there is no set values for main earth, just main protective bonding, minimum 6mm for tns,tt and minimum for tnc-s 10mm,

the valuers are in the book if you cant be bothered too count

except it is a minimum of 4mm2 for any unprotected protective conductor according to 543.1.1.
 
  • Like
Reactions: 1 person
With TN-C-S the minimum is 10mm², as the earth conductor is treated the same as a bonding conductor.
However, a smaller CSA could be deemed as adequate, if there is no evidence of overheating.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wirral
Business Name
Farm electrics

Thread Information

Title
Adiabatic formula
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Farmelectrics,
Last reply from
Deleted member 26818,
Replies
9
Views
4,889

Advert