Just going through my EIC that i will be summitting to BC- then to use this job for my Niceic initial assessment- so just trying to make sure theres no holes!

job is just new ring circuit to 2 sockets out a 32a mcb on 30ma rcd side of a existing 16th board.

in sec 3- comments on existing installation

i have put 'unable to verify charactoristic of primary over current protective device- suppliers property'
-them put LIM in section 8 for supply protective device.
and 'incoming water main is plastic on supply and consumer side of stop cock- recommend installing bonding to 1st point of copper pipe where reasonably practical.'

in sec 6- any departs

i have put 'absence of circuit schedule for fuse board (c3) Absence of testing and inspection notice (c3)'
 
if its all plastic, i wouldnt even recommend bonding it

for only two socket outlets, i personally would of used a 20A radial, but nothing wrong with a ring


sounds ok
 
And the assessor will probably be wondering why you would run a ring to serve just two sockets as it suggests a lack of design ability/knowledge.
 
  • Like
Reactions: 1 person
And the assessor will probably be wondering why you would run a ring to serve just two sockets as it suggests a lack of design ability/knowledge.


Originally plan it to be a radial as you say its only 2 sockets

then it was decided thermal insulation was being used in the stud- changing my ref from c to 103!

instead of buying bigger cable 4/poss 6 i decided to keep the 2.5, do it as a ring and have 20a as ocd

ccc for 2.5 in 103 is 13.5a x2 (ring) 27a

thats why its a ring


if i was to leave as a radial as ref 103- ccc would of been 13.5amp and would of had to go on 10amp ocd


made the best out of a bad situation that i couldnt help!

if i explain the above with conviction- will that not show competence?
 
just put N/V in the box.
 
If its 60/80 put 60a, if its 100a put 100a
 
You are not allowed to use 'LIM' on an EIC

I see that this has been debated before on this forum . I note that reg 634.2 (referring to limitations) is only under 634 Periodic Inspection & Testing. I've looked through GN3 (green version) and can't find the reference to not using 'limitations' in an EIC.

Using the online certification provided by Elecsa (think niceic use exact same software by Certsure), the only selectable option for rated current for the primary supply OPD is, either the rated current (i.e. 100a), N/A or LIM. It won't allow you to put anything else in there. 'LIM' is also an option for all the other characteristics for the primary supply OPD.

'LIM' is also an available option in the 'test results' section.
 
  • Like
Reactions: 1 person
No there's no reference to not using LIM, just as there's nothing stating you can't use a 6" nail as a fuse.
BS7671 is a standard, not a list of what not to do or a how to book.
 
The old schedule of inspections (red book) included a note to say that LIM was applicable to periodic inspections only.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

J.C.E

Arms
~
Joined
Location
Earth

Thread Information

Title
Advise on my EIC to be used on niceic assessment
Prefix
NICEIC Certification Scheme 
Forum
Certification NICEIC, NAPIT, Stroma, BECSA Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
J.C.E,
Last reply from
Richard Burns,
Replies
15
Views
2,772

Advert