Just going through my EIC that i will be summitting to BC- then to use this job for my Niceic initial assessment- so just trying to make sure theres no holes!
job is just new ring circuit to 2 sockets out a 32a mcb on 30ma rcd side of a existing 16th board.
in sec 3- comments on existing installation
i have put 'unable to verify charactoristic of primary over current protective device- suppliers property'
-them put LIM in section 8 for supply protective device.
and 'incoming water main is plastic on supply and consumer side of stop cock- recommend installing bonding to 1st point of copper pipe where reasonably practical.'
in sec 6- any departs
i have put 'absence of circuit schedule for fuse board (c3) Absence of testing and inspection notice (c3)'
job is just new ring circuit to 2 sockets out a 32a mcb on 30ma rcd side of a existing 16th board.
in sec 3- comments on existing installation
i have put 'unable to verify charactoristic of primary over current protective device- suppliers property'
-them put LIM in section 8 for supply protective device.
and 'incoming water main is plastic on supply and consumer side of stop cock- recommend installing bonding to 1st point of copper pipe where reasonably practical.'
in sec 6- any departs
i have put 'absence of circuit schedule for fuse board (c3) Absence of testing and inspection notice (c3)'