Hello everyone,

Just getting familiar with the changes to BS 7671 brought in with Amendment 3. I have a question regarding Regulation 411.3.3 in particular.

The Regulation states that an RCD should be provided for socket-outlets with a rated current not exceeding 20A for all installations. With an exception to omit RCD protection for a specific labelled socket-outlet, or where, other than for an installation in a dwelling, a documented risk assessment determines that the RCD is not necessary.

So my question is this, does this regulation only apply to new installations or will all existing circuits serving socket-outlets need to be retrofitted with RCDs or omitted through risk assessment?

I work in a fairly large industrial plant with many, many socket-outlets!

Looking forward to any responses.

Thanks
 
applies only to new installs. that would cover from adding a single socket to an existing circuit to a full new installation. itis not retrospective as regards existing parts of the installation, but would be given an appropriate code on an EICR.
 
As Above ...There is no need to change your existing sockets , you would only need RCD protection for any new sockets that you fit to an existing or new circuit unless as you say the socket you are installing is for specific use ,labelled and risk assessment done
 
Hi, so just to re-touch on this topic again. I do a fair amount of installation work (if you can class it as such) :rofl: in conservatories for a company local to myself. Quite often splitting the existing ring main to incorporate additional outlets/lighting. Am I correct in assuming each new outlet only should be protected by an RCD socket or FCU? It doesn't apply to the whole circuit being worked on?

Many thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Lancashire

Thread Information

Title
Amendment 3 RCD question...
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
mrhorse,
Last reply from
Browny-89,
Replies
4
Views
1,820

Advert

Back
Top