M

mayfair

Hi Guys
Been to a warehouse today large cooler room main MCB 40A 4 pole N L1L2L3 plus 40A 30ma Diff it all works fine until the compresor shuts off then the Main MCB trips ...not the diff the mcb if you put i back on all is fine even if compresor dont start. Any thoughts my brain hurts.
Cheers
Gary
 
1 sec

so its the mcb tripping but not the rcbo?

can we get a picture please?


are you sure its not a rcd main switch?
 
surely you would have a bigger main switch than rcd though. and we have been using rcd main switches recently[emoji20]
 
One thought, it could be possible when the compressor for the fridge stops the stat is energised because it needs to take over to maintain the temperature and it could be faulty and shorting out hense the short circuit and the fact the MCB is blowing, then again it may be something completely different.
 
  • Like
Reactions: 1 person
Is the compressor contactor operating anything when in the off position like a sump heater or defrost element that could have a fault maybe?

Can you upload some pics of the controls?
 
  • Like
Reactions: 2 people
will do thanks for your input
Is the compressor contactor operating anything when in the off position like a sump heater or defrost element that could have a fault maybe?

Can you upload some pics of the controls?
 
Looks like (Fingers crossed) it was the thermostat arcing not done it since it was changed at 8.00 am this morning still dont know why the rcd didnt drop out ramped it and seems ok. As my old lecturer used to say its fixed be happy with that and stop foofing around with it now. Thanks for input apart from #2 which i still dont understand
 
Looks like (Fingers crossed) it was the thermostat arcing not done it since it was changed at 8.00 am this morning still dont know why the rcd didnt drop out ramped it and seems ok. As my old lecturer used to say its fixed be happy with that and stop foofing around with it now. Thanks for input apart from #2 which i still dont understand
So I was right then?
 
  • Like
Reactions: 1 person
Does this now mean Im a 1day fridge engineer.......Sod that give me some a graet big DB to wire up any day of the week
 
Glad it's up and running again although I'm not sure why an arcing t/stat would be the cause. I enjoy refrigeration work, it's interesting controls and it makes a nice change to the run of the mill stuff.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Any ideas Please
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
mayfair,
Last reply from
Marvo,
Replies
11
Views
1,743

Advert