i have just completed an installation where i have installed a second consumer unit to supply some small circuits to a kitchen and shed.this second consumer unit is fed from a spare circuit breaker in the main consumer unit and is rcd protected.i have tested all the circuits and everthing is ok.i am unsure how to fill in the certs.is the feed to the new unit classed as a distribution circuit or an extension of the circuits in the main unit.i was considering filling in two seperate eic.one for distribution to new consumer and one for new comsumer and circuits.if i did this would i put on the form"supply conductors" the feed cable size ie 6mm any help greatly appreciated.i need to get it right as i intend to use as a test job
 
There should be a box at top of circuit designation page that says "If not fed from origin please state details" or something along them lines.
 
This would be a sub board and will require two schedule forms with the test data. One for the single circuit on the supply board showing the details of distribution circuit, and the second "Sub Board - Fed from......" showing all of the circuits contained within.
 
THANKS FOR THAT,DOES THIS MEAN THAT ON THE EIC FOR THE SUB BOARD IN THE "MAIN SWITCH OR CIRCUIT BREAKER" SECTION THE SUPPLY CONDUCTOR SIZE WOULD BE 6mm and not 25mm as is the main supply
 
There should be a box at top of circuit designation page that says "If not fed from origin please state details" or something along them lines.

That's on NIC forms.
 
Not knowing what forms you use, but I use electronic versions. The EIC covers the supply (Main Incommer) and the top of each schedule there is also a box for the board main switch. As part of an EIC, you will have to detail the main supply, earthing and bonding, so start at the supply fuse and work through it logically.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Certification of installation
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
waynelester,
Last reply from
Graeme Harrold,
Replies
5
Views
1,250

Advert