Discuss Code 1 Problems - Am I being Scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Is the board change on advise of the letting agency that they require all the properties to have RCD protection ?

I know that quite a few uni's and agencies have a stipulation that all properties must have RCD protection, I just wonder if your agency stipulated same, and the sparks was informed of this?

Saying that the 150 pound price for an hours work does seem excessive, and his coding does leave a lot to be desired. Can't make out why he has LIMITED the 2 circuits on the IR test, and still managed to carry out an R1 + R2 on them.
 
That cert is a duffer, he must have measured the Zs and subtracted the Ze for the R1+R2 readings as readings are all consistently 0.22ohms difference.

I think you are right to refuse to pay for a PIR that is wrong in so many ways.
 
those readings look like they were copied out of a book.
 
As telectrix alluded, he may have been a plumber in disguise.

Check anyone you get in to quote on here Local Authority Building Control - HOME

Hmmm, an unknown 2.5mm circuit with a 16A breaker, no idea what that is likely to be in a domestic environment given what else has been identified :banghead:
maybe there is an immersion heater lurking away where it can't be found.
 
Thanks for all the replies guys. I will be using all of this when speaking to the electrician later. One thing that does spring to mind. On my driveway I have a montion sensor activated lamp which comes on when anyone is within the vicinity of the front door. Could this be why he has given a Code 1 on No RCD protection?
 
Thanks for all the replies guys. I will be using all of this when speaking to the electrician later. One thing that does spring to mind. On my driveway I have a montion sensor activated lamp which comes on when anyone is within the vicinity of the front door. Could this be why he has given a Code 1 on No RCD protection?

I doubt it unlessit has a 13A socket built into it which you can plug your mower into!
 
Why has the box been ticked for presence of RCDs, then a code 1 been applied for lack of RCD protection?
I'd also question the use of N/A in the boxes for SELV, Electrical separation, Segregation of Band I and Band II and segregation of safety circuits.
I would have thought that the door bell would be SELV and Band I, and the smoke alarm circuit would to my mind be a safety circuit?
 

Reply to Code 1 Problems - Am I being Scammed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello ! I am building for some time a cct to drive a 3digit multiplexed LCD. (from aliexpress) From the sellers on aliexpress I managed to find...
Replies
7
Views
1K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
800
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
502
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
898
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock