Hi everybody,

Ok, here is the picture.

Main house is TN-S
Ze is 0.25 ohms

There is a 16mm swa fed from a 60a isolator, which in turn is fed from 25mm tails into henley blocks.
The swa is clipped outside the side of the house, buried in the garden and along approx 25 meters into a small studio / storage area.

There, there is an 8 way c/unit. 100a main switch, 2x RCD's. 1 RCD controls the storage sockets ( 4 ) and the studio florescent tube.

The other RCD controls the sudio room sockets ( 4 ) and the storage florescent.

My mate who just completed the install, calls me and tells me that he is getting 1.17ohms when doing a Zs on the sockets !!

I go and see. The cables and sockets are in plastic trunking, so no problem there. I check again the Zs on the install at the c/unit and get 0.35ohms. Ok fine.

I remembered once, an old school sparks, who on site where we worked, had a similar problem and he changed the RCD's and got a lower Zs reading.

I pulled out 2 legrand 30ma RCD's from the van, connected them up, and low and behold Zs is now 0.43ohms on sockets !!!

I did carry out an insulation resistance test and final ring tests prior to connecting new RCD's, which all were ok, as its a new install.

Any thoughts, can this really lower the Zs ??? Do RCD's play a part when checking Zs ??

Thanks and regards,
Sav
 
I have seen this loads of times. I occasionally help my mate out on rewires etc, and he insists in using cheep consumers units where if you add the R1 & R2 to Ze they are often 0.5 - 0.6 ohms lower than the Zs taken with the meter. This inaccuracy can only be down to the RCD. I use different consumers units from him and never see that level of difference.

Ian
 

Reply to Hi Zs solved by changing RCD ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
467
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock