I get confused with this.

am I right in saying, anything that was according to the old regs which is not in the current regs passes the EICR.


Do I have to mention this as a C3 improvement recommended on the EICR. Its for insurance purposes.

the new forms ask for too much!!!!!!!!!!!!!


Another question. Do I have to use another set of forms for each board as if it was another installation or can i use same forms with added test schedule sheets for other boards.
 
Last edited by a moderator:
one test result shedule for each lad, one iinspection schedule, number all pages ;_
 
There is not and never has been a particular requirement in BS7671 for RCD protection to be placed in a DB.
As such the lack of such protection does not warrent a code.
There is a requirement to provide RCD protection for circuits of locations containing baths or showers, which would require the RCD protection to be positioned in a DB, but the comment and any code would refer to the lack of RCD protection for those circuits, not that the DB did not contain an RCD.
Yes it is generally accepted that an unaltered installation that complied with the Regulations at the time of construction or design, would pass, even if it doesn't comply with the current edition.
Obviously there are some instances that would not, such as protective devices in neutral conductors, or where a shower has been installed in a bedroom.
If there have been any additions or alterations, you would have to confirm that at the time, they also complied.
I would use a separate schedule for each board.
 
Last edited by a moderator:
Couldnt have worded it btr Spinny Tomany "PIR guys" put stuff like "No RCD protection " without specifing why ect and they cant see backwards ie 15th 16th regs have changed over the years making things "safer" (IMO relying to much on and emfasis on RCDs being the beall and endall of protection) and to many guys doing PIRs dont think backwards nor do they think about what they are coding or putting in faults iv seen PIRs that list things by the reg but not describing how it fails to comply the client hasnt got a clue what reg " 34,5,69" is others put whats wrong but couldnt look up regs if required n just say "i know its not right " but dont know WHY its not right
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Industrial place with 3 phase board, no RCD protection, does it pass?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
electricshock,
Last reply from
mogga,
Replies
7
Views
2,903

Advert