Hi

I am thinking about having 4 racks of very power hungry servers in a room in my house. Each rack needs 25KW, plus 10KW for other household uses uses (Kettle, hairdryer etc.). Obviously the electrics box and fuses are going to have to be upgraded but I was wondering if it is possible and allowed for me to a have a 100-110KW supply to my detached house or will this place to much load on a residential electricity substation?

Thanks in advance
 
Have another look at the handbook for the servers! 25KW each, you have missed something somewhere.

Most of the power will be lost in heat dissipation. 100KW in one room the solder will be running off the PCB’s. So added to the household load add 130KW for air conditioning.

PS. The UPS system will take up another room. It will weigh several tonnes. Then there is the standby generator. Where you put that is up to you!

You are looking at a three phase 400A supply to a house.

View attachment 12970

Before going on line with this system have a Google search for a reality check!
 
  • Like
Reactions: 5 people
On the bright side you wont have to shell out for central heating though a good fire alarm system might be advisable.
 
Have you worked out the bill for using 24x100 kWh each day?
 
http://www.electriciansforums.net/a...10kw-residential-property-writing_process.gif

LMFAO lol.

Turns out the server came with the wrong manual. I only need 9KW for now which should not be a problem. Thanks for the posts anyhow.

Is it normal to have three phase 400A to a small commercial property (on an industrial estate for example), or is only single phase.

Just wondering what size of a commercial property I would have to buy to get this type of connection for future reference.

Thanks Again
 
Looking at £12 an hour to run the servers if 100Kw was the case (based on 12p per 1kwh unit)
 
http://www.electriciansforums.net/a...10kw-residential-property-writing_process.gif

LMFAO lol.

Turns out the server came with the wrong manual. I only need 9KW for now which should not be a problem. Thanks for the posts anyhow.

Is it normal to have three phase 400A to a small commercial property (on an industrial estate for example), or is only single phase.

Just wondering what size of a commercial property I would have to buy to get this type of connection for future reference.

Thanks Again
Small industrial or commercial would normally have 3ph 100Aamp supply and a quote from the DNO for a upgrade would be needed as the variables means a estimate wouldn't be possible without indepth knowledge of the local substations, demands etc, larger commercial and industrial may have 200A-400A incommers, but it all depends on the previous company or the buildings preposed use as to what you will get, you would have to make enquiries as its a question we cant answer as every building is different with a different history and approx' to sub-station.
 
LMFAO lol.

Turns out the server came with the wrong manual. I only need 9KW for now which should not be a problem. Thanks for the posts anyhow.

Is it normal to have three phase 400A to a small commercial property (on an industrial estate for example), or is only single phase.

Just wondering what size of a commercial property I would have to buy to get this type of connection for future reference.

Thanks Again

I would think it highly unlikely that a small to small-medium industrial unit will have anywhere near a 3 phase 400A supply available. I think you'll be very lucky to get a 200A supply!! lol!! They will also probably want to penalise you, for contaminating the local DNO distribution TX with harmonic currents...lol!!
 
Hi, Have you got a link handy for a technical spec for these servers, or some similar? I'm struggling to imagine how a peice of IT equiment like that could possible require 9KW per rack..? thanks!
 
40A server rack !! YES INDEED!! some of our servers are power hungry 3 phase (dual supplied) monsters!

at the place i work (HP DATA CENTRE) we are currently pulling in the building

@ 20:59 = Total KW 3555.0 / IT Load KW = 2425.4
 
Just out of interest, what exactly are you planning to do with these 'servers'?
... Or is that a secret?
 
i would assume he would be a internet developer and quite possibly use them to store data, or resell the space on the server to clients!!!
 
I was referring to the fact its in his house. Ive installed many a server room 100A upwards but never in the spare room :-)
 
my stupid mate installed a server in his back bedroom of his parents house!! dont ask me why!!! but i spoke to him couple months ago and he has to keep a window open and even has portable aircon unit in there as temps exceed 30+ within minutes!!
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Is it possible to supply 110KW to a residential property?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
undernet,
Last reply from
DNS1,
Replies
30
Views
4,295

Advert