Thanks ?. That's what I'd come up with but wasn't sure if it needed extra capacity, a bit like a pump starting up.14 kWatt. 240 x 60 = 14,400. watts. that size of heater would be best on a 3 phase supply. then it's only 20A/phase. and of course, 2.5mm cable as opposed to 10mm.
No, an immersion heater is normally a purely resistive load.wasn't sure if it needed extra capacity, a bit like a pump starting up.
OP it depends what the supply voltage is14 kWatt. 240 x 60 = 14,400. watts. that size of heater would be best on a 3 phase supply. then it's only 20A/phase. and of course, 2.5mm cable as opposed to 10mm.