I'm glad they have cleared up that TIC = DNC but still means companies could put the TIC and DNC as the inverter rating. Even if it shouldn't be the case, all FIT suppliers I think now ask for the number of panels and total wattage of each panel on the FIT application form so really TIC and DNC need to be the peak rating of the panels regardless of the legal nature of the definition of TIC.

I like the idea of putting the cost information into the certificate as it means DECC aren't using sample data from 10 companies to form the basis for their future policies. If pv prices increase and this is reflected in the MCS certificates over the next 3-6 months then at least DECC will have access to up to date information. Although i am not sure what it means by ' the cost does not need to cover anything other than the cost of the MCS certified product'. Do they mean we should only put in the cost of the PV panels for Solar PV?

All the other new requirements don't really bother me either way.
 
Although i am not sure what it means by ' the cost does not need to cover anything other than the cost of the MCS certified product'. Do they mean we should only put in the cost of the PV panels for Solar PV?

I would hope not, since the data is being used by DECC to monitor installation costs. I would suggest it's a vaguely worded attempt to find out the cost of an MCS accredited solar PV installation. Otherwise, it's a pretty meaningless measure for DECC.
 
I would hope not, since the data is being used by DECC to monitor installation costs. I would suggest it's a vaguely worded attempt to find out the cost of an MCS accredited solar PV installation. Otherwise, it's a pretty meaningless measure for DECC.

Then they should be more clear with their wording. You'll get some companies putting in TIC as the inverter and some as the panels then some will put the total installed cost of the system and some will just put the cost of the panels.

I'm more than happy for us to put our total installed costs down on the MCS cert if it means DECC have up to date costs.
 
My discussions with the head of the MCS unit at gemserv were unambiguous and very concise.

If you install an inverter capped at 16A then the TIC = 3.68kW irrespective of the kWp of the panels.


The SSEG is the inverter (that's what has to be installed to G83 / G59 etc) the panels are purely the power source, in the same way that a pile of coal is for a coal fired power station.
 
Completely agree, but have MCS put that in writing and told all registered installers that that is what they should do when completing the cert?
 
@TedM, nope, you need to pin them against a wall at one of the exhibitions etc they attend! :33:
 
My discussions with the head of the MCS unit at gemserv were unambiguous and very concise.If you install an inverter capped at 16A then the TIC = 3.68kW irrespective of the kWp of the panels.The SSEG is the inverter (that's what has to be installed to G83 / G59 etc) the panels are purely the power source, in the same way that a pile of coal is for a coal fired power station.
Is this his/her opinion or MCS/gemserves position? As ofgem and decc as of may last year thought and stated TIC= panels. All fit suppliers ask for number of panels and peak wattage now so its ofgem and deccs position that tic = panels
 
Hi, could someone explain to me the "self certification through a CPS" within the building regs compliance section? Ive never done this before, thank you in advance
 
Also relates to Part A - be careful with your response, not all MCS certification bodies are equal ...

CPS = Competent Persons Scheme.
 
My question si though....

On a commerical contract if the client sources themselves the panels, mounting, system, cables and inverter etc, as specified by the MCS certified installer, Then what price would you enter, as you would have no idea... - Also applies to social housing or new development jobs...
 
Is this his/her opinion or MCS/gemserves position? As ofgem and decc as of may last year thought and stated TIC= panels. All fit suppliers ask for number of panels and peak wattage now so its ofgem and deccs position that tic = panels

Seeing as I had the head of the MCS division from Gemserv, his employees and Ofgem sitting at the same table at the time, - and I asked him twice this was clearly not a personal opinion, it was clearly the "MCS Licensee's" offical position
 
Did the OFGEM representative at that meeting not respond to this statement? If not I could only surmise that they did not realise the significance of what was being said, or maybe they were experiencing temporary 'professional deafness'.
 
Ofgem fully understood EXACTLY what was being said, as I put forward the idea of an east / west 2 x 2.5kW system as the example... They declined to give an answer though, and didn't "correct" Gemserv, despite being prompted to comment at least twice...

Also re my comment on cost of system above, I've just registered a new site on the database, and the instructions tell you to put 0.00 in for the price untill they have clarification of what DECC want it for :)
 
My discussions with the head of the MCS unit at gemserv were unambiguous and very concise.

If you install an inverter capped at 16A then the TIC = 3.68kW irrespective of the kWp of the panels.


The SSEG is the inverter (that's what has to be installed to G83 / G59 etc) the panels are purely the power source, in the same way that a pile of coal is for a coal fired power station.
unless you have that in writing it's meaningless.

I have it in writing from the head of the renewables section at Ofgem that they do not accept this is the case, and were instructing Gemserve to that effect.

Cost me about a grand in refunds, and £2.5k in legal fees as well did that dispute before we were forced to give up challenging them.
 
Though it's very interesting that you've had that opinion verbally from MCS in that setting. I might go back to Ofgem with that statement and see if they've changed their position again.
 
I have it in writing from the head of the renewables section at Ofgem that they do not accept this is the case, and were instructing Gemserve to that effect.

Although OFGEM have said that to you, both OFGEM and Gemserve in their formally published guidance to date have been quite careful not to contradict the legislation as I interpret it (ie the same way as Worcester). Gemserve are just a commercial company providing a service and will be quite careful to make sure they do not do anything that will leave them liable downstream. OFGEM I regret are a) covering their arris not wanting to admit a mistake they have made in interpreting the legislation and hoping the issue will go away and b) probably think they are doing the right thing minimising solar pv fit payments after all the initial furore even if that is not what the legislation says nor what they have formally been instructed to do.
 
Although OFGEM have said that to you, both OFGEM and Gemserve in their formally published guidance to date have been quite careful not to contradict the legislation as I interpret it (ie the same way as Worcester). Gemserve are just a commercial company providing a service and will be quite careful to make sure they do not do anything that will leave them liable downstream. OFGEM I regret are a) covering their arris not wanting to admit a mistake they have made in interpreting the legislation and hoping the issue will go away and b) probably think they are doing the right thing minimising solar pv fit payments after all the initial furore even if that is not what the legislation says nor what they have formally been instructed to do.
ah, but they have covered themselves in the guidance, as it says something about getting confirmation from Ofgem about it - so unless anyone's got written confirmation from Ofgem that this is allowed in the way they're interpreting it for solar PV, then it's fairly meaningless unfortunately if Ofgem get involved at a later stage.

As I say, unless anyone has this in writing from Ofgem, then anything that may have been discussed verbally counts for precisely nothing in Ofgem's eyes.
 
These are the LEGAL definitions as published by the Government:

from here: https://www.gov.uk/government/uploa...file/65653/6778-fits-modifications-4-2012.pdf
being the latest legislation

“Total Installed Capacity” means the maximum capacity at which an Eligible Installation could be operated for a sustained period without causing damage to it (assuming the Eligible Lowcarbon Energy Source was available to it without interruption), a declaration of which is submitted as part of the processes of ROO-FIT Accreditation and MCScertified Registration;

“Declared Net Capacity” means the maximum capacity at which the installation can be operated for a sustained period without causing damage to it (assuming the source of power used by it to generate electricity was available to it without interruption) less the amount of electricity that is consumed by the plant;


Solar panles are simply the low energy carbon source.

You need to refer to the inverter manual to establish the "maximum capacity at which an Eligible Installation could be operated for a sustained period without causing damage to it"

Of course there is a bit of a **** up here, as the inveter isn't specified or registered on the MCS certificate, and for some reason or other it is the panels that are .....

With an AD plant, you don't have to get your maize crop or waste veggy mater certified to MCS standards ... Its the device that converts the methane into electrciity that is certified and rated ....

So if you have 3Kwp of MCS certified Solar PV panels hooked up to an SMA 5000-TL your TIC should be 4.6kW
and if you have 5kWp hooked up to a Power-one PVI-3.6 then your TIC will be 3.68kW

I can find no-where in writing that TIC relates to panels - GavinA would you crae to share your written sources / guidance document please?
 
worcester - I agree with all of that, and have expensive legal opinion that also agrees with it. Unfortunately, when it came down to it, Ofgem refused to comply with the legislation or their guidance, and instead asserted that DNC, TNC referred to the panels only, and essentially dared us to take them to judicial review to prove them wrong.

if you're going to work on that basis I'd seriously advise you to make sure you always have £10k+ in an account that you're willing to use only to cover the basic costs of judicial review to prove your point, if not then it could come back to haunt you.

I eventually wasn't able to challenge it due to financial constraints, and had to give it up, remove a panel and compensate our customer for the difference as it was cheaper than taking Ofgem to court.
 
I have not completed one since they changed the MCS form.

Can anyone tell me whether the new form includes a section whereby each installation must include building regs from the local council?

Thanks
 
It asks how you are complying with Building Regs. Irony Part P isn't needed for our typical commercial installtions, as it's covered under the Electricity at Work Act :)

Seems like the new MCS resgistration process assumes domestic work ...
 

Reply to New MCS Certificate in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

My best mate has been medically retired from the prison service at the young age of 52 and has time on his hands :D He's looking at a 'plug in'...
Replies
7
Views
504
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
Replies
3
Views
421
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
732
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock