Just did an EICR on a 3 phase DB that had feeds from the board all exit together through a bush and lockring, go to a rotary isolator mounted to the trunking next to the board and then the loads from the rotary’s passed through a different bush in the board and to a seperate bit of containment. The cables are 4mm or 6mm twin and earths supplying 4 32A SP commando sockets would this be an issue with eddys?The requirement is for the enclosure to be flame retardant, no mention is made of the cable entries. If you use stuffing glands with T&E you should really replace the rubber inserts with those that have oval holes through them. T&Es on ring finals can pass through separate entries. Wouldn't be worrying about using plastic wall plugs.