Piratepete

Hi Guys.
Main heating in a new build bungalow is 3 storage+convector heaters and 2 convector heaters. I haven't installed storage heaters before.

I understand that if a fixed heater is rated more than 2Kw, you should put it on a seperate radial circuit (can someone tell me where I've read that?).

The storage heaters are 2.55Kw and 2 at 1.7Kw which could all be supplied on 2 off 20Amp radials to the Offpeak board.
The convectors are 6.25Kw (27 Amps) in total, which could all be wired into their own 32Amp ring to the normal board.
Is this bad practice? Are they all normally on their own radials? If so, would it be acceptable to provide 3 radials for the storage sections but still keep the convectors on their own ring?
Cheers!
 
Last edited by a moderator:
i would say that its normal practice to wire the storage heaters radially, each heater having its own radial circuit and i cant see why the convectors cant be wired into their own ring main as you suggest
 
Check out appendix 15 it refers you to regulation 433.1.5 about loading a ring final circuit. One of the recommendations for not exceeding the load current capacity on the cables of a ring is not connecting oven hobs and cookers over 2kw and not fitting immersion heaters, space heating which is NSH or loads of a similar profile.

So the normal installation of a NSH system are individual radials. Protected by a 16amp PD and connecting via a FCU
 
or, a 32A 4mm radial for each of the 6.25kw heaters.
 

Reply to Storage/convector Heater Circuits? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
164
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
223

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock