Im pricing some external lighting on several industrial units which are all joined. One long length of conduit will suit although its around 150-200yards long. Nice straightforward run with no bends. Its around 8m high and away from any mechanical damage, my only concern is sun damage over time.

Galvanised conduit would be best but a) its going to add a considerable cost to job and b) its going to take much longer to install.

is white PVC ok , should I install black PVC, or should I risk losing the job pricing for galvy ?

The customer will likely want cheapest.
 
White HIP for me. Black does look better but I have had it fading badly after a couple of years.

Or SWA
 
I would use armoured cable on the inside of the units myself, surface conduit will not be the best method for this project. However if you are determined to do it then I would use galv conduit myself, Armoured along the inside is the best method though hands down IMO
 
  • Like
Reactions: 2 people
problem we have is we are not to disturb residents of units. We have an external supply so no reason at all to enter. I like the idea of conduit because it would be easy to add more lights later, Im pretty certain he will do this.
 
  • Like
Reactions: 1 person
Well I have lost count of the Business units I have wired up and never run conduit 150-200 mtrs around the front that's for sure, still you asked for views, I gave mine.
 
Are these units all one company or are they separate business's

Separate , we have a landlords supply for a large pump so will be using that meter to supply small 2 way board , contactors and dusk till dawn sensors. The front of the building is around 200yards long but its an nice easy straight run
 
Well I have lost count of the Business units I have wired up and never run conduit 150-200 mtrs around the front that's for sure, still you asked for views, I gave mine.

Of course , not my usual field so advice welcome.

its actually the back of the units and not particularly pleasing on the eye so for aesthetics I'm not too concerned.

I am coming round to the idea of armour now Ive thought about it .
 
Another problem with pvc conduit can be expansion,seen quite a few long runs where they have sagged during the summer,ends up looking a right mess.
 
  • Like
Reactions: 3 people
Allways price both options. Gives you two bites of the apples then.

Proberly lose job to some tw&t that does it in surface twin anyway :devil2:
 
  • Like
Reactions: 4 people
Well if you have to use tube you will be better off using galv, plastic will move about all over the place over a period of 2-3 winter/summers and look awful eventually.

- - - Updated - - -

Another problem with pvc conduit can be expansion,seen quite a few long runs where they have sagged during the summer,ends up looking a right mess.
beat me too it phil lol
 
  • Like
Reactions: 2 people
Well if you have to use tube you will be better off using galv, plastic will move about all over the place over a period of 2-3 winter/summers and look awful eventually.

- - - Updated - - -

beat me too it phil lol
That's 'cause I wasn't stood in the corner with a party seven lol
 
  • Like
Reactions: 3 people
Well if you have to use tube you will be better off using galv, plastic will move about all over the place over a period of 2-3 winter/summers and look awful eventually.

Prefer steel myself, but with expansion couplers the PVC shouldn't look quite so crap!
 
200 yards of cable down conduit, you will have considerable volt drop on that. Having you done your calcs to work out if you will get the cables down a conduit?
 
Not sure if it applies to conduit but black flex is preferred outside due to its superior UV qualities. Which I always struggled with because I was taught that black absorbs heat and white reflects so could never get why black flex was better outside until I looked it up. And its deeper than that.

so wondered if it applies to conduit too.

Maybe thats why SWA is black
 
  • Like
Reactions: 1 person
SWA all the way , IMO< wirh ad. boxes at eacht fitting on flex
 
  • Like
Reactions: 2 people
really long runs of pvc conny end up looking cack over time..........

galv will triple the cost............

swa or fp200 for the win !
 
  • Like
Reactions: 1 person
Galv conduit all day long and did do a very similar job last year looked well, remember a tin of galv spray for vice markings on tube and I spray saddles as well if external seen them rust prematurely
 
Galv will be easier to dress along 200yards than swa
 
  • Like
Reactions: 1 person
SWA into galv t boxes with a stuffing gland at each fitting for me please? Volt drop will need to be considered as mr B stated.
 
5x 80w LEDs , so minimal load.. thinking 1.5mm should be ok but will likely run 2.5 to be safe. Not even sure contactor will be required , may split load into 2 DTD or perhaps even one will do need to check switching load been while since fitted one ?
 
starting to think armour would be pretty quick , 2 men cherry picker , chalk line , hold , clip hold, hold , clip ....gland...box light , hold clip hold clip...

At my pace Ill rattle 200 yards in a day ;P

- - - Updated - - -

1.5? 200 mtrs? hmm

200 yards , around 180m , but like I said will likely do 2.5 anyway
 
Me likes galvo, plastic if you have to, swa possible, micc love it,fp never worked with it.
 
quoting around 4k including VAT,

Require x5 80w LEDs, few drums or armour or conduit plus singles, accessories etc.

Cherry picker for 1 week , all very basic runs and routes ....

what you think ?
 
FP is useless as far to soft!, galv would be my choice, if it's a straight run then it's about 65 lengths, with a thro box every 9m, you can get away with saddling galv on a horizontal plain every 800, where as SWA will need clipping every 300 on the horizontal, two of us could put that lot up and have it wired in 3 days.

SWA is your other alternative but be warned, 6x2.5 and 3x 1.5 conductors in a t box will be bordering on a bit tight.
 
quoting around 4k including VAT,

Require x5 80w LEDs, few drums or armour or conduit plus singles, accessories etc.

Cherry picker for 1 week , all very basic runs and routes ....

what you think ?
Well without actually costing the materials myself I cannot confirm the price either way, however first impression it seems a good quote actually, works out about 3,250 ish plus vat.
 
3" galv tray on stand-offs then cable tie SWA. future proofing for any new cable runs.:drool5:
 
Well without actually costing the materials myself I cannot confirm the price either way, however first impression it seems a good quote actually, works out about 3,250 ish plus vat.

sounds like you've recovered from your sourcreamflow binge.
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Which conduit ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
134

Advert

Thread statistics

Created
Guest569,
Last reply from
Knobhead,
Replies
134
Views
13,773

Advert