0
Hi guys, I have wired light fixtures and hard wired a lot of cookers in the past, been all fine.

I'm now training to be an electrician, the course itself is level 1 electrical installation.

I have just bought my first continuity tester which is a fluke T90 and wondering if this is good enough to test on light fixtures after wiring to see if it's good to go before turning it on?

Thanks for any answers.
 
answer is No. you'll need a MFT to perform both dead and live tests, including RCD trip times. then you need to complete installation certificate which entails software.
The T90 will check for Volts, and continuity, but for anything else as Per Tels post
 
hi pete. glad to hear about your recovery from your ex health problem.

you now have full permission to join the Borg Collective. :D:D:D.
 
hi pete. glad to hear about your recovery from your ex health problem.

you now have full permission to join the Borg Collective. :D:D:D.
Thanks for that Tel, any idea when the next cube will be coming this way?
 
i have it on reliable authority that it will make an appearance at Elex manchester next year... oops.misread the email it's not the Borg, it's NICEIC
 
Thanks guys. I've played about with it, well not literally 'played' but you know what I mean. I've tested it in a socket when circuit is live and got 230v. Tried the 2 pins of a b22 ceiling lamp holder while circuit is live, with switch on and off and got 230v when on and does nothing off.

When I try the terminals I get 230v both ways switch on and off, circuit is live.

With circuit off and placing the probes on terminals I think it just does the same as what it would when testing the fluke by putting the two probes together. I guess the current is just going through the fixture and making the fluke do the test thing.
 
basically, if you put the probes on a live circuit, the t90 will measure volts. L-N, L-E,N-E. on a dead circuit it will give an indication of continuity. it's basically a bang tester.
 
Thanks buddy. I was thinking I could use it after wiring the lamp fixture, circuit on but switch off, and see if it gives me 230v or continuity.

The terminals I were referring to were on a light fixture, turned off by the switch but the lighting circuit was still on by the main circuit board.
 
if the light as are wired 3 plate, the even with the switch off, 1 trminal will still be "live"

aplogosys for the beer spilling spellinge.
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
 
the main funshun od thr t90 is to prove dead or nit.

is ti fat fungres or beer/? ? tihink ill'goo two bed.

spicswervers tomnirrows/
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.

Yes it will come in handy. You always need a voltage indicator or safe isolation.
I appreciate you are just starting out in your training, but reading section 6 of the regs may help with the required tests, and also Chris Kitcher does some clear informative videos on testing ..

chriskitcher - https://www.youtube.com/user/chriskitcher
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
It’ll be more than handy John,it’ll save you from pain and you can’t work on electrical installations without proving dead and safe isolation procedure so you’ll use it a lot
 
Thanks again. The reason I thought I would be ok to check with it to see if it's safe is because at college we have been using fluke t5 1000's on the lights we put up on the wooden boards. Been doing one way, 2 way, 2 plate and 3 plate. One light on a board with a consumer unit, using a t5 1000 to test the light. At college though we twist some of the consumer units wires together before testing. Left unconnected from the unit.
 
Thanks again. The reason I thought I would be ok to check with it to see if it's safe is because at college we have been using fluke t5 1000's on the lights we put up on the wooden boards. Been doing one way, 2 way, 2 plate and 3 plate. One light on a board with a consumer unit, using a t5 1000 to test the light. At college though we twist some of the consumer units wires together before testing. Left unconnected from the unit.

Are you on about R1+R2 testing for continuity of cpc? Would be very surprised if you are being taught to do this using a T5 tester rather than a proper low ohm resistance meter.
 
We arent being tought resistors in series in practical but are in theory. I can not remember which wires we connected but earth was one of them. We tested in ohms, did not really pay attention to out else.
 
To cut to the chase, say if I wired up a new lamp holder to the ceiling (yes lamps glow bulbs grow lol). If I were to use a tester to see if it is safe and good to go or not, what tester would I use? If there is such tester for such purpose. It's not that I lack confidence, I'm neat when I do stuff and never had a problem. I've Wired variac transformers and put them in cases, lights, cookers and a few other things I can't remember doing but have experience with wires and know being neat is very inportant.

To be honest my course at college has been a mess. We have been juggled about having different tutors pretty much every few weeks and because some students misbehave a lot for some tutors, some weeks at college are a joke. I think at college things should be moving at a quicker pace to be honest. If I want to get to level 2 I have to work hard and revise lots outside college.

One tutor tried explaining about testers a few theory sessions ago but most of the class was just being a pain basically.

Really appreciate the replies, every little helps. Will do a lot of browsing around on here, see what's to learn...
 
Last edited:
As mentioned before John you can’t “test” a circuit with voltage indicators other than proving live or dead, buzzing out identifying cables when you can’t see its entire run by joining 2 cores of a cable together at one end and then testing for continuity at the other end continuity is confirmed by your voltage indicators buzzing/beeping....same as testing R1+R2 but you’d need a multi function tester to perform that “test”
 
Sorry that is a carp video, there are others not the T90 but similar in make, up have a look, Just search "how to use a Fluke T90" plenty of other vids, must admit I never watched the one I sent you until after I posted, a Carp video sorry about that.
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
Your T90 should be used a lot for Isolation purposes
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
Your T90 should be used a lot for Isolation purposes
Hi guys, I have wired light fixtures and hard wired a lot of cookers in the past, been all fine.

I'm now training to be an electrician, the course itself is level 1 electrical installation.

I have just bought my first continuity tester which is a fluke T90 and wondering if this is good enough to test on light fixtures after wiring to see if it's good to go before turning it on?

Thanks for any answers.
John Welcome, If you are currently in training, you could do no better than apply to gain access to the trainee area, doesn't matter how dumb your question may sound to you , or how simple the answer may be, you will get help, without the fear of being ridiculed, for not knowing something, apply to one of the Mods "Westward 10, Sparkychick, Leesparkykent, there are others but it's early and I haven't woken up properly yet, good luck.
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
Your T90 should be used a lot for Isolation purposes
Hi guys, I have wired light fixtures and hard wired a lot of cookers in the past, been all fine.

I'm now training to be an electrician, the course itself is level 1 electrical installation.

I have just bought my first continuity tester which is a fluke T90 and wondering if this is good enough to test on light fixtures after wiring to see if it's good to go before turning it on?

Thanks for any answers.
John Welcome, If you are currently in training, you could do no better than apply to gain access to the trainee area, doesn't matter how dumb your question may sound to you , or how simple the answer may be, you will get help, without the fear of being ridiculed, for not knowing something, apply to one of the Mods "Westward 10, Sparkychick, Leesparkykent, there are others but it's early and I haven't woken up properly yet, good luck. You also get a colored icon by your name to donate you as a Trainee,
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
Your T90 should be used a lot for Isolation purposes
Hi guys, I have wired light fixtures and hard wired a lot of cookers in the past, been all fine.

I'm now training to be an electrician, the course itself is level 1 electrical installation.

I have just bought my first continuity tester which is a fluke T90 and wondering if this is good enough to test on light fixtures after wiring to see if it's good to go before turning it on?

Thanks for any answers.
John Welcome, If you are currently in training, you could do no better than apply to gain access to the trainee area, doesn't matter how dumb your question may sound to you , or how simple the answer may be, you will get help, without the fear of being ridiculed, for not knowing something, apply to one of the Mods "Westward 10, Sparkychick, Leesparkykent, there are others but it's early and I haven't woken up properly yet, good luck. You also get a colored icon by your name to donate you as a Trainee,
 
Thanks, yes it is 3 plate mate.

Was hoping I got the right kind of tester but nevermind. It's become more clearer what i've got and what I need now that i've been on here so thanks guys.

It will come in handy one day no doubt.
Your T90 should be used a lot for Isolation purposes
Safe isolation video for you to get your head around JW makes some very good instructional videos
 
but will he get a Crackerjack pen?
Crackerjack, not many people will know what Crackerjack was Tel, a pity really I know I liked it, never got a pen though, got a Jim'll fix it badge, but NO he never fixed anything for me, thank you very much.
 
Thanks so much, just woken up and this got to 3 pages already. I understand the purpose of this tester now and seems there isn't a tester for the purpose i'm looking for.

Again thanks very much. Also I have enough pens ta ;)
 
Thanks so much, just woken up and this got to 3 pages already. I understand the purpose of this tester now and seems there isn't a tester for the purpose i'm looking for.

Again thanks very much. Also I have enough pens ta ;)

Of course there is a tester for the purpose you are looking for, I'm not clear what that purpose is though yet.
A MFT is the popular choice for most electricians to perform required tests for safety and for fault finding.
 
Purpose is to test a new fitted and wired lamp fixture in the ceiling before turning it on. I've just been looking at nultifunction testers, more expensive but may still get one. I know exactly what the T90 is for now and will come in handy in the future. We were told at college that in level 2 the students are advised to buy one anyway.
 
have a look on ebay for 2nd hand megger mft with calibration. usually get a good one for around £300. or keep an eye open on the forum. occasionally 1 comes up for sale by a member.
 
Not a very good college lol. It's been a joke the way the course has been ran. I won't go further in detail though lol it'll be quite an essay.

I've changed all the lights with no trips etc, all came on first go. My new flat is now complete, got all the lampshades on now.

I will browse around here and see what else I can find online about whatever topic we're doing at college, considering the slow pace we're learning at college especially.
 

Reply to Can a fluke T90 continuity tester be capable of confirming a new light fixture is good to go or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, just joined the forum, have a weird problem, wondering if I could get some ideas. We built our house about 6 years ago. The downstairs...
Replies
2
Views
1K
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
814
Evening all. Been at a property the last couple of days that had suffered damage due to a surge. I got the power back on all circuits apart from...
Replies
17
Views
2K
I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit...
Replies
3
Views
941
Hi, just wondering how other sparks, go about confirming main earth bonding continuity when supply cannot be isolated, ze and pfc can be enquired...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock