S
Steve-S
H5 relating to an immersion heating over 15 litres of water says:
Should be supplied by their own separate circuit.
No mention of sub circuits, nothing. A final ring with 13A mcb off the ring, then a 20A switched-cord outlet connection unit complies. It then has its own separate circuit. A circuit not shared with any other outlet or appliance.
photo by Westward10
20A switched cord outlet below:
  • Optimistic
Ok, 1 post from me and then I’m done here.
My only comment is that bs7671 appendix 15 gives advice about ring final circuits and suggests that various large loads over 2kw should be on a dedicated circuit. While not mentioned by name, immersion heaters draw more than the items that are mentioned.
I believe it’s been established that the regs don’t allow you to put an MCB on the ring.
Strictly and pedantically speaking it may not be against normative regs in BS7671 itself to connect an IH directly to the ring using a 20amp isolator, omitting over currrent protection for a fixed load. However the overall compliance of the ring relies on less than a 20amp load on any section of cable, and having a high current drawing device on the circuit for large chunks of time reduces the capacity of the rest of the circuit by a good margin.
Plenty of guidance documents and the informative appendix advise against doing this.
So please enlighten us - why would you want to do this?
Consumer unit, 16amp MCB, cable, 20amp DP isolator, job done. I don’t understand any motivation to do otherwise?!
photo by Westward10
May I suggest you familiarise yourself with part 2 (definitions) of the regs.
A circuit is defined quite clearly in there, a seperate circuit is therefore a separate one of those.
The definitions as used/defined by the regs are what we all must follow, so learning those would be far better than random understandings by others merely trying to remember them.
Not even getting involved. It's the same pointless thread as the last one.
Circuit: An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s).
This is really basic stuff and the OP is clearly a liability to themselves and others. These threads remind me of that old adage "a little knowledge is a dangerous thing".
Reactions: SparkyChick and DPG
photo by Westward10
On to something more interesting, how do you feel about beards, are you for or against ?
Mr Howard,
"I believe it’s been established that the regs don’t allow you to put an MCB on the ring."
It has not been established.
If there was a 30A breaker at CU, a 4mm radial circuit then a 13A single socket off it and a 13A FCU at a 3kW immersion, there is lots of amps available, but that is not a separate circuit as it is shared.
But a 13A MCB off a final ring, a cable, then a 20A switch and cord outlet, then separate circuit has been created. It may be a sub circuit but clearly separate. Does it meet regs tough?
One scenario is an upstairs final ring. It will take most of the time a TV and a few computers - nothing at all. The biggest load will the a vacuum cleaner every now and then. I see no reason why a 3kW immersion cannot be taken off the ring. The ring will never come anywhere close to 32A.
Nephew has had a substantial solar array installed. There was no immersion cable run to the upstairs cylinder by the builder 20 years ago as it was heated an still heated by gas. So he naturally wants to heat it via electricity for free a lot of the time. On a cloudy day he can pull in around 3kW. To get a cable to it will be a nightmare when a little used final ring is adjacent. Electrically and safety-wise there is no problem, only the regs may get in the way.
Splitting the ring may be an option.
Will do.
Exactly what I outlined. At the ring an over-current device at the origin then a separate radial circuit created supplying only one appliance. All circuit protected by the over-current device.
There is nothing to stop a competent designer from doing whatever they want, as long they note it as a deviation on the certification, and declare that it is no less safe than it would be if the design was done strictly to BS7671.
I picked up this.. Looks to conform to BS 7671.
Every circuit must be separate from others and must be connected to its own overcurrent protective fuse or circuit breaker in a switch fuse, distribution board, consumer's unit, etc.
Perhaps the OP should pose these questions to the IET.
The key word is separate. It is common to see a sub CU off a say 40A beaker in the main CU. Similar arrangement is also done with garage CU units. So a 40A circuit has a number of sub circuits off it with one maybe being an immersion. So an immersion then does not have its own circuit back to the main CU. It is a circuit off a circuit, but regarded as separate and all above board. No different to taking an immersion off a final ring with its own mcb at the take off point.
Reactions: Avo Mk8
Looks like a sense of humour is banned on this forum now then!
The key word is not separate it is final.
Sub circuit is not a currently recognised term, circuits are either final circuits or distribution circuits.
A distribution circuit is a circuit which feeds a distribution board or consumer unit which then in turn feeds other circuits.
A final circuit is a circuit which feeds final points of utilisation, either lighting points, sockets or fixed current using equipment.
A ring final circuit is, by definition, a final circuit and not a distribution circuit.
Thanks. However it says:
"Should be supplied by their own separate circuit."
It does not say final.
Yes a separate circuit, if it is not a seperate final circuit then it is not separate.
A distribution circuit is a type of circuit which, by definition, feeds multiple separate final circuits via a distribution board or consumer unit.
A final circuit does not feed any other circuit.
A ring final circuit cannot then feed another circuit.
Reactions: nicebutdim
Really needs the definitions in the regs to pin it down.
Yes I agree with you.
You should go and spent some time revising.
The Wiring Regulations contain clear definitions for both distribution and final circuits in the section appropriately titled 'Definitions'.
I have not found anything yet to counter my initial assessment. I may do, you never know.
It's not hard to find as 'Definitions' are afforded their own section in The Wiring Regulations - 'Section 2'.
Not so much a case of not having found anything yet, but one of deliberately ignoring regulatory instruction which does exactly what you 'haven't been able to find'.
You can read and understand The Wiring Regulations or you can continue to ignore them and form more of your own mad ideas - quite frankly it makes no odds to me. At this point I'm simply looking forward to the rapidly approaching moment when these threads stop appearing on this forum.
Reactions: DPG and Julie.
Mad is creating a new circuit to take an immersion off? my oh my! Such Entrenched views.
The IET write The Wiring Regulations - as previously suggested it would be best to take this argument up with them. So far not a single member of this forum has expressed an opinion in favour of your idea, so it's unlikely that continuing to repeat the same action will yield a different result.
Reactions: DPG and SparkyChick
Maybe I'm missing something but my reasoning is that there is only one reg about ring final circuits:
An MCB isn't an accessory to BS 1363.
Thank you for giving the context. That would be a much better topic for a thread as about 10 questions immediately come to my mind.
If he ever adds battery storage and wants to use a solar diverter, he will want a dedicated circuit that the solar diverter can simply turn on and off, and he won't want the upstairs ring turning off when the batteries aren't fully changed.
Also, I believe that with solar diverters, the load must be resistive.
Reactions: timhoward
Taking a radial off a final ring with its own ocpd (MCB or fuse):
1) Creates a circuit that can have more than one outlet.
2) Having more than one outlet the circuit is shared by the outlets hence not separate.
3) A separate circuit is serving only one outlet.
I have seen nothing yet to negate that above.
  • Optimistic
I think the first thing to attempt to understand is the word “separate”.
If you plug an iron and a washing machine into a ring final circuit are those items on separate circuits or both on a ring final circuit ?
I'll do my best to explain why I think your intended approach is flawed:
The regs document BS7671 has only one reg about ring final circuits and honestly it's pretty vague, amounting to use one of these protective devices, and this cable, and make sure you won't exceed the current carrying capacity of the cable for long periods.
To complement this there is an appendix 15 in BS7671 specifying ways to comply with the one regulation (433.1.204)
That says that the requirements can generally be achieved by (Fig 15a ii ) "Not supplying immersion heaters, comprehensive electric space heating or loads of a similar profile from the ring circuit." (direct quote, page 555)
Indent iii also advises to run dedicated radial circuits for various large loads over 2Kw.
To further complement the regs there is the on site guide. If you follow this to the letter you are likely to comply with the actual (more complicated) regulations.
As you have stated, the OSG also says to put immersion heaters on a separate circuit (paraphrased)
It makes no sense at all to interpret the OSG as you suggest as it would completely undermine appendix 15; the power is still coming from the same ring final circuit along the same cables, and the stated intention is not to exceed the ring final circuit's CCC for long periods.
The actual compliance comes down to the loading of the circuit, and it may be safe and comply today. It also may not be safe another day if the heating fails and the fan heaters come out.
This all amounts to a choice. You either do an installation that follows the advice in the regs and the on-site-guide that any competent electrician won't question, or you do something unusual that future electricians will do a double-take at, instantly think of the sentences in black and white in two places that advise not to do this, and get them wondering if it's compliant.
Even if you go ahead, I'm intrigued what your intention is for controlling it? Would he have to go upstairs when it's sunny and turn it on?
If he ever adds battery storage and wants to use a solar diverter, he will want a dedicated circuit that the solar diverter can simply turn on and off, and he won't want the upstairs ring turning off when the batteries Yes a thread in its aren't fully changed.
Yes, a thread in its own is worthy.
In this case far more than 3kW can be generated which the surplus power over 3Kw (immersion heater size) will be used by the whole house and not exported back to the grid. In short, all the solar electricity will be fed into the whole house.
An iBoost can be fitted adjacent to a cylinder. The iBoost monitors export to the grid, and when export is about 25 watts, the iBoost sends solar power it to the 1st immersion output (to immersion), when the water temp reaches max temperature, it then switches to the 2nd immersion (the bottom one). Then when the both are at max temp, the iBoost allows for export to the grid. If the iBoost has no water to heat it can only allow export. This is fine when having a cheaper fuel like gas available. When solar available a relay can be on the output of the iBoost to switch out the gas boiler.
Thx.
Still it is full of recommendations, advice, etc. Nothing firm.
A point you bring up "future electricians will do a double-take".
I did a search on this forum finding one thread from a few years ago, that an electrician would not connect up an immersion as a control unit consuming hardly any current at all was to be taken off the same adjacent supply. The circuit was a dedicated radial from the CU with a 16A MCB. Of course the circuit was then shared, not separate. I realised that one way around it was to make the cable from CU a distribution circuit to a small CU at the cylinder with a 13A MCB for the immersion and an MCB for the control box. Hassle and expense to placate an awkward electrician which added no extra value in safety, but sorted.
Thinking on those lines A 4-way metal CU off the ring with a double pole 16A MCB. Off the MCB a 13A MCB for immersion and a 3A for the iBoost. But I think the iBoost is powered from the incoming immersion supply. That should stop a double-take.
Thx.
The more you think, the worse it gets.
An explanation of how you intend to wire this maybe helpful.
An option is off the upstairs 32A ring take a separate radial protected by a double pole MCB feeding the iBoost which switches from top to bottom immersions. Then a relay on each output of the iBoost to switch out the gas boiler. The iBoost communicates to its CT at the CU by wi-fi.
Gas boiler heats the cylinder to 56C with blending valve down to 53C for the DHW outlet temp using a blending valve. The iBoost will heat the cylinder to 75-80C, clawing as much free solar electricity as possible. If the sun is out first thing heating the cylinder, and the cylinder is depleted of DHW because of morning showers, the gas is cut out and the solar stays on heating cylinder.
I do hope you're not actually doing electrical work.
This is the thorn in your side and not just for this design but seems to be for any design you think up.
The manufacture states that:
1. The electrical installation of this device must only be undertaken by a suitably trained and qualified electrician.
All local safety standards must be observed.
All work must satisfy Building/IEE Wiring regulations in force at the time.
Email
Time zone
Last seen
Definition of own circuit
Steve-S,
Steve-S,