Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm cable on to a second double socket.

The question is, who would be happy to leave this arrangement in place, and who would downgrade the breaker to 20A? I would say it's ok, as the 2.5mm can't be overloaded as it feeds only one double socket, just like an infused spur off a ring.
 
be fine as it is.
 
Thanks Tel. Still don't know why they didn't just use all 4mm though, talk about penny pinching.
 
  • Like
Reactions: Admin
maybe it was a sunday. or wholesalers 20 miles away, or wholesaler wanted to sell him 100m when he only needed 1m.
 
  • Like
Reactions: Admin
IMO okay, not much difference than a spur off a RFC IN 2.5mm.
 
As others have said, sounds similar to a spur off a rfc so can't see an issue with it. I wanted a bit 4mm yesterday, Screwfix don't even stock it - it's a next day item. Not to mention I've just bought a nice shiney new circular saw, opened it up, doesn't even come with a blade. Bah humbug.
 
  • Like
Reactions: Admin
Nope wrong in my eyes especially when someone sticks another point on it. What cable is the 4.0
 
I think it's reg 433.2.2
My thought would be to add another 20A mcb and move the 4/2.5 radial onto that. Win win?
Yes, this is what I suggested in my OP, but the other branch is running some fairly big loads, which is why I wanted to avoid it.
 
What do you mean what cable is the 4.0? It's bog standard 4mm+1.5mm cpc T&E. Length 1m. If someone adds another socket from the 2.5 in future, that's their look-out.
Well 4mm could equate to many cable types.
 
  • Like
Reactions: kingeri
nothing wrong with it, if someone want to add to it later he has to upgrade it, apart from that its been installed correctly
 
nothing wrong with it, if someone want to add to it later he has to upgrade it, apart from that its been installed correctly
Poor practice, but there you go.
 
if you look at Fig 15B BYB it shows a 32a 4.0mm radial with a unfused spur to double socket via j.b. wired in 2.5 .I would rather like to see it in 4.mm or on own 20A prothctive device.
 
I will C2 it all day.
 
The cable is not suitably protected against overcurrent, this is how I see it.
 
In design terms cable must carry less than or equal to the protective device. i.e. 32a protecting a 17a ccc does not meet this criteria. Look up Ib In Iz and try not to make me do it please :) Dammit...433.1.1
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2.5mm on 32A MCB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68

Advert

Thread statistics

Created
kingeri,
Last reply from
GMES,
Replies
68
Views
13,662

Advert